Adding 100amp Subpanel For Basement - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 06-11-2010, 06:26 PM   #16
Take a look at the below image:
http://img823.imageshack.us/img823/3561/img0339.jpg
I am planning to remove the small piece of wood that connects the two studs. Also, I made sure the studs are far apart to meet the min clearance.
Reg the two yellow wires and black wire. I shall be removing the two yellow ones to create the space for double pole breaker. The black wire is the earth wire and cannot be removed.
trajendra_babu is offline   Reply With Quote
Old 06-11-2010, 06:33 PM   #17
Master Electrician
Rewards Points: 3,920
Originally Posted by a7ecorsair View Post
In the 90 deg column is lists XHHW-2 as 100 amps. so if the 100 amp breaker is 90 degs. then it should be good. Check with your inspector though.
You cannot use the 90 deg column for wire ampacity unless all of your terminals are rated for 90 deg. Most are rated for 75 deg. C. If it's SE or SER you must use the 60 deg C. rating which is 75 amps for #2 AL.
brric is offline   Reply With Quote
Old 06-11-2010, 06:40 PM   #18
What about going out the bottom ?
Old 06-11-2010, 07:05 PM   #19
Where can I find the ratings for the terminals?
Old 06-11-2010, 07:52 PM   #20
Master Electrician
On the breakers or the label on the panel. It does not matter. SE and SER cables can only use the 60 deg C. rating which is 75 amps..
Old 06-12-2010, 07:33 PM   #21
I had a electrician visit today. He suggested that there is no need to add additional panel. I need 10 additonal breakers to finish the basement. He suggested to replace some of the breakers with one inch two pole breakers.
Is this acceptable? BTW, its a GE 200amp panel with 32 breakers.
Also, here is top view of the panel. How can I get 10 additional wires into the panel?
Any suggestions?
Thanks in advance.
Old 06-12-2010, 08:20 PM   #22
I=E/R
a7ecorsair's Avatar
You have a 200 amp panel with 32 breakers and you need 12 more circuits?
a7ecorsair is offline   Reply With Quote
Old 06-12-2010, 09:54 PM   #23
I need 10 more breakers, not 12 (to finish off the basement).
Adding a subpanel to a sub-panel and other questions CardinalPilot Electrical 14 03-30-2011 02:23 PM
Have questions about adding a 60amp subpanel humberguy Electrical 6 05-13-2010 07:57 AM
Adding Subpanel for Basement - Few Questions mindle Electrical 28 01-07-2010 08:49 AM
adding subpanel in attic -- is this feasible? jayp Electrical 8 05-22-2009 10:22 AM
Adding a subpanel BimmerRacer Electrical 20 04-01-2009 08:30 PM