add breaker to ge tlm3020c
I have full panel and need two additional 15amp breakers. Door indicates I can use 1/2 size breakers but cannot find specs on box to determine if I can put 2 half size in one full size slot. Is there an "approved" solution or do I need a secondary panel? I would rather not look under every breaker to see if any can be doubled.
arejohn is offline   Reply With Quote
Old 01-07-2011, 12:20 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 380
Most newer GE panels can take slim breakers anywhere in the panel.
Old 01-07-2011, 12:50 PM   #3
Master Electrician
Rewards Points: 3,808
My TM2030 allows THQP(1/2") breakers on the bottom 5 locations on both busses for a total of 10 locations.
brric is offline   Reply With Quote
Old 01-07-2011, 02:05 PM   #4
This one is 15 years old. I will check the bottom breakers.
I know it takes 1/2" but can I double them?
Old 01-07-2011, 03:02 PM   #5
Master Electrician
Yes. A one inch space allows two 1/2" THQP breakers. Be advised this will only provide two 120 volt circuits, not a 240 volt circuit.
The Following User Says Thank You to brric For This Useful Post:
arejohn (01-08-2011)
Old 01-08-2011, 04:47 PM   #6
Thanks guys. Only looked at bottom 3 left side and all will take 2 half size breakers.
Old 01-09-2011, 10:35 PM   #7
Electrical Supplier
Rewards Points: 150
You can get whats called "non-CTL" breakers to make the 1/2 sizes.
However unless the bottom few tabs have slots in them that look different from the rest your panel is not SUPPOSED to have these half size breakers.
ALL panels made today are whats called CTL panels. Unless they specifically designate the ability to have more circuits with spaces, you arent supposed to put in "tandems" or half size breakers.
"Do it right the first time and avoid duplication of effort"
Your AHJ/Inspectors ALWAYS have the final say on ANY electrical code issue.
If in doubt, contact a licensed, experienced, reputable electrician to perform the work.
LyonsElecSupply is offline   Reply With Quote
Old 01-10-2011, 12:35 AM   #8
Panel is from 1995. Lower three full size slots have contacts that look like this
-|-. Would like to think what I am doing is up to code. I am not adding any additional current load. I need dedicated circuit for 110v gas furnace that replaced 220v gaspack. Since I am in there I am going to add dedicated circuit for communications equipment.
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 11:36 AM
Breaker box wiring question(s) janralix Electrical 6 08-29-2010 10:13 PM
Breaker Tripping Jeridmar6 Electrical 15 07-10-2010 08:20 PM
20 amp GFCI breaker pops when pool pump is turned on. jagrunner Electrical 11 03-19-2010 04:31 PM
Sq D Trillaint Breaker problem jmreynol Electrical 3 04-28-2009 07:06 PM