Old 03-07-2010, 07:09 PM   #1
Is it acceptable to use push connectors AND screws on a duplex receptacle?
I'm replacing a painted duplex receptacle and noticed that it has wires connected to the screws AND the push connectors. It appears to me that the receptacle is being used as a junction to feed another conductor. It is not switched.
There are a total of three 14-2 conductors in the box.
Is it acceptable to junction on the receptacle itself? Or, should all junctions be made with wire nuts within the box? Is there a suitable reference in NEC2008?
Bob K. is offline   Reply With Quote
Old 03-07-2010, 07:16 PM   #2
Master Electrician
I don't do it but there is no code prohibition against it.
brric is online now   Reply With Quote
Old 03-07-2010, 07:19 PM   #3
This post may be addressing the same subject but I couldn't be sure without pictures: receptacle: 1 romex in 2 out?
Old 03-07-2010, 07:24 PM   #4
retired elect/hvac/plumb
plummen's Avatar
omaha does not allow using the plug as a joint anyway ,joints must be pigtailed with a wirenut before attaching to the plug
plummen is offline   Reply With Quote
Old 03-07-2010, 07:38 PM   #5
joed's Avatar
It is acceptable but not advisable since pushins are a very common source of open connections.
You can buy receptacles that are back wired. The wires go into holes and then are clamped by tightening the screw. This type can accept four wires. Here is one sample. Image doesn't show the back wire.
http://electrical.hardwarestore.com/...et-102896.aspx
Do not PM with questions that can be asked in a forum. I will not respond.
Old 03-07-2010, 08:14 PM   #6
Thank you. I decided to pigtail for the new receptacle.