Above Ground Pool Circuit - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 07-27-2012, 09:16 PM   #16
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Originally Posted by electures View Post
First, New Jersey is using the 2011 NEC unless you specified the 2008 NEC when you filed for the permit. Second, romex is only permitted "inside" the dwelling (Speedy Pete will disagree). However, I know several inspectors in NJ who will not accept romex outside. Ask your local EI before you start. GFI protection is only required on up to 20amp 120/240 volt circuits. What size is the motor?
What do you mean by outside? The simple fact of inserting the cable into the back of a bell box? I wouldn't consider that outside either. If you do, you better show me a WP breaker for a 3R panel. lol....
And I have also heard of electricians that when a 1 1/2 HP pump installed they opt for the 25 amp breaker. sneaky.
Old 07-27-2012, 09:19 PM   #17
Motor is 1HP - 110V.
Juance is offline   Reply With Quote
Old 07-27-2012, 09:20 PM   #18
E2 Electrician
i would convert the circuit to 240v if possible.
Old 07-27-2012, 11:33 PM   #19
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
The wire entering the bell box is outside the dwelling. 690 only allows romex inside. Sounds like nit picking but code is code. I know several inspectors in new jersey who will not accept it.
As for the 1 hp motor, the breaker can be as high as 40 amp and gfi is not required for anything over 20 amp.
Under the 2008nec #14 can be used. Under the2011 #12 has to be used.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 07-28-2012, 07:33 AM   #20
E2 Electrician
Mike Holt used to have a graphic showing this exact installation, and I agree that it's nitpicking, so playing devils advocate, if I cut in an old work box, for the pool pump receptacle, that would be accepted? Just not a bell box that is also fastened to the structure?
Old 07-28-2012, 07:51 AM   #21
Rewards Points: 242
Not to hijack but I had a similar thread about a month ago had a lot of good info in it about requirements:
Underground Run To Outlet For Pool. LB fitting out of siding?
collegetry is offline   Reply With Quote
Old 07-28-2012, 08:40 AM   #22
electures's Avatar
Good point. Earlier this year I asked Robert McCollougha (misspelled) who is past international president of IAEI and chairperson of the cmp for article 680 about this exact scenario. He told me that if you follow the letter of the code, romex is not permitted outside the the dwelling. He also thought it was nitpicking. However, since the op is from new jersey, and there are EI,s here who follow the letter of the code , I felt I should warn the op.
The Following User Says Thank You to electures For This Useful Post:
stickboy1375 (07-28-2012)
Old 07-28-2012, 08:48 AM   #23
E2 Electrician
I'm curious if the CMP's only intention was for pools installed indoors or the wording just got lost on paper of the true intention of what they were allowing? IMO, the NEC would be twice as thick if they actually had to spell out every little intent of code sections like this one...
Old 07-28-2012, 11:05 AM   #24
electures's Avatar
Even if they did that people would still disagree. This is where experience comes in to play. Look at how many unqualified people think the handbook is code.
On another note, the 1 1/2 hp pump motor you referred to earlier cannot be connected to the 20a twist lock. It's a violation.
Old 07-28-2012, 11:08 AM   #25
E2 Electrician
I'll bite, how so?
Old 07-28-2012, 11:13 AM   #26
electures's Avatar
I'll bite, how so?
Lol. Check out 430.109 (G). The twist lock is required to be horsepower rated. A 20a twist lock is rated up to 1 hp. Can't use it on a 1 1/2hp motor.
Old 07-28-2012, 11:18 AM   #27
E2 Electrician
2005 NEC
430.109 (G) Torque Motors. For torque motors, the disconnecting means shall be permitted to be a general-use switch.
Is there a cross reference to the 2005?
Never mind, it's 430.109 (F)
Thank you by the way.
Old 07-28-2012, 11:22 AM   #28
electures's Avatar
2005 NEC
Sorry. Quoted from memory.
Old 07-28-2012, 11:25 AM   #29
E2 Electrician
I was just about to edit my signature about people shooting from the hip with code sections, too.
Old 07-28-2012, 11:29 AM   #30
electures's Avatar
Hey I was off by one sentence. Better then quoting "page ?? of the 1500 page book". Lol.
in ground pool bonding vasben Electrical 134 01-16-2016 12:26 PM
Need to know if my grounds and neutrals are connected right dorlow Electrical 185 01-15-2012 02:54 PM
Tripping breakers,neutrals,120 volts and 240 volts OH My!!! Stubbie Electrical 17 06-11-2011 06:09 AM
Need new circuit for pool filter/pump gifer Electrical 3 09-19-2008 03:13 PM
Slab Ground pool inspection alexromu Electrical 6 08-06-2008 07:01 AM