7.5 Hp Motor - Electrical - DIY Chatroom Home Improvement Forum
Old 01-14-2013, 12:20 PM   #1
7.5 hp motor
I am looking at wiring up a 7.5 hp 230 volt 31 amp motor in my garage for a steamer. I beleive I will need #8 copper to wire it up with a 75 amp breaker. I would like to be able to plug it into the wall. What should the amperage of the receptacle be? My thinking is if I sell the place and someone decides to plug in a heater or something that it could be a problem.
in-need is offline   Reply With Quote
Old 01-14-2013, 12:55 PM   #2
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
According to the NEC the motor need will conductors rated for 40A. #8 copper will comply. The breaker can be as high as 100A. You really need to consult the manufacturers installation instructions for what they require. If you decide to cord and plug connect it, the plug and receptacle have to be horsepower rated.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 01-14-2013, 01:12 PM   #3
Thanks I appreciate your quick response. Just so I am clear the plugin 15-50R horsepower rated would comply with the code?
Old 01-14-2013, 01:16 PM   #4
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
The conductors need to be 1.25 x the listed amperage in the NEC motor tables for single phase motors. So a single motor branch circuit would need 1.25 x 40 amps = 50 amps. I you use thhn individual conductors in a listed conduit like emt #8 awg copper will work. NM-b cable will not comply with 50 amps.
I doubt you will need the maximum amperage breaker which is 2.5 times the table value of 40 amps or 100 amp inverse time breaker. The idea is to hold the start-up current long enough for the motor to return to running amps under load. Anyway I would be surprised if you needed anything over 50 amps to start the motor though 75 will work if that is what you already have.
The branch circuit is rated by the breaker installed on the circuit so if you stick to a 50 amp breaker you could find a 6-50 receptacle and plug at the store and not have to find a special plug at an electrical supply.
What is the method for starting and stopping the motor?
Old 01-14-2013, 01:19 PM   #5
UAW SKILLED TRADES
Stubbie's Avatar
Are you talking about a 3 phase motor ? If you are then we need to rethink the previous replies?
Old 01-14-2013, 01:26 PM   #6
electures's Avatar
You have to check with the manufacturer and find out the horse power rating. A 15-50R is HP rated for 3 HP. A 6-50R is HP rated for 3 HP. I can't find anything rated for 7.5 HP, 1 ph. You may have to hard wire it.
Old 01-14-2013, 01:37 PM   #7
It is single phase 240 volt 7.5hp 31 amp
Old 01-14-2013, 01:40 PM   #8
electures's Avatar
I checked the Hubbel website and the largest 1ph plug/receptacle HP rating is for 3HP.
Old 01-14-2013, 01:42 PM   #9
Thanks electures, I was looking at the 3 phase receptacles not the 1 phase.
Old 01-14-2013, 01:43 PM   #10
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
I think you should use an inexpensive manual starter. That way you'll have motor overload, short circuit protection, and a disconnect all in one.
wirenut1110 is offline   Reply With Quote
Old 01-14-2013, 06:31 PM   #11
UAW SKILLED TRADES
Stubbie's Avatar
This is why I'm asking what he is going to use to start and stop the motor. The receptacle and plug only needs to be horsepower rated to equal the motor ratings if it is the disconnecting means.
Tags
single phase motor , wiring motor
How to replace condensor fan motor? twags HVAC 44 08-27-2015 05:09 PM
Please HELP wiring 240v motor for forward and reverse on boat lift mikeyce Electrical 6 10-16-2012 01:27 AM
Old Rheem Air Blower Motor Wiring Problem CompoundNetwork HVAC 3 11-20-2011 03:51 PM
Air Handler Motor Wiring brando1118 HVAC 13 06-18-2010 11:42 AM
Replacing a Condenser Fan Motor thothtp HVAC 5 06-08-2008 06:30 PM