#1 |
60AMP Subpanel Wire Size/Type Question
Newbie here. I do woodworking in my garage as a hobby and have several tools there. With 2 electric space heaters on I keep tripping the existing circuit and need to upgrade. I want put a subpanel in my garage which is attached to my house via a breezeway. I live in PA.
I will be starting from an existing 200AMP Square D QO panel where I plan to install a 60 AMP breaker. Wire will run roughly 50' through my basement ceiling, run 10' under ground (easier than going through upstairs walls) in conduit, then run 15' in the garage. So roughly 80' total. I plan to attach it to a 100AMP subpanel, probably QO120M100C (OK?). What size and type of wire will I need? Will I need conduit with this wire in the house, or just underground? I am considering 6-3NM-B ($2.56/ft at HD) and stripping the cover off the underground/conduit section (HD suggestion). A second option is 6/3THHN ($2.32/ft at local elec store). I'm trying to stay with 6AWG due to cost, 4AWG is a bit over my budget. Will either of these work? |
#2 | ||
DIYer
60AMP Subpanel Wire Size/Type QuestionQuote:
You need to keep the neutral and ground separate in the subpanel too. This panel just has one neutral bus. |
#3 |
Electrical Contractor
You can not use nm-b for the underground part. You must use 6/3 uf , or transition to conduit underground.
Yes I am a Pirate, 200 years too late. "Jimmy Buffett" |
#4 |
60AMP Subpanel Wire Size/Type Question |
#5 |
You still can not use nm-b outside. You must use uf(then you do not need conduit), or use thwn and use conduit all the way from panel to panel.
#6 | |
#7 |
Electrician
Just a couple comments...
Gigs suggestion of a main load center without a main disconnect in the garage may not fly...first check with your AHJ as to whether your garage is still consider 'detached'...the breezeway may not make it 'attached'. If it's considered 'detached', it will need a main disconnect and a ground rod or two. If it's 'attached' it won't need either of those. To add to jbfan's comment of transitioning to underground conduit...the underground wires have to be rated THWN. Most THHN type wire is multi-rated (THHN/THWN/MTW, etc.) but check it first. You can run NM up to a junction box and then transition to a conduit run which would have the THWN wires in it.
Kyle Just because you can, doesn't always mean you should Last edited by SD515; 11-26-2008 at 10:01 AM. |
#8 |
Using that panel will be fine. The wire will be protected by the breaker in the main panel, and the 100 amp breaker just becomes a disconnect for the garage.
#9 |
Thanks. Would appreciate more comments from others on this. I'll be using conduit for the 10 feet outside whatever I go with.
#10 |
Licensed Pro
Doesn't matter... you cannot use type NM cable in a wet location, which underground in conduit is. And it is never acceptable to "strip the cover off" of NM to make it acceptable for use in conduit. Another "HD suggestion" that is totally wrong.
If this garage is detached, you need a panel with a main breaker, a four wire feeder, and a ground rod. If it is attached, you may substitute a main lug panel, you still need a four wire feeder, but no additional ground rod is required. I would use 6/3 NM for the portion inside, transition to THWN for the conduit portion (3-#6, 1-#10), and continue in conduit to the subpanel; OR run 6/3 UF the whole way, with no conduit underground. You guys type too fast!
"Life is hard. Life is harder when you're stupid." John Wayne Last edited by HouseHelper; 11-26-2008 at 10:04 AM. Reason: slow typer |
#11 |
#12 |
[quote=HouseHelper;190384]OR run 6/3 UF the whole way, with no conduit underground.
quote] If I go with UF, can I put the UF in conduit for appearances sake. It will be running on the outside of my building for 2 feet before it hits the ground. |
#13 |
I do want a cutoff in the garage. Good to keep the equipment safe from minors (if my daughter ever has kids).
#14 |
[QUOTE=xv144;190390]Yes. You must protect the wire where it enters the ground, and where it exits the ground.
#15 |
[quote=HouseHelper;190384]I would use 6/3 NM for the portion inside, transition to THWN for the conduit portion (3-#6, 1-#10), and continue in conduit to the subpanel; OR run 6/3 UF the whole way, with no conduit underground.[quote]
This sounds reasonable. If I go this way I'll have to price the THWN and UF and see how things work out. You guys are great. |
| Display Modes | |
| subpanel question | Brik | Electrical | 2 | 11-30-2008 06:31 AM |
| Can i add a subpanel fed by 10/2 wire? | qst4sno | Electrical | 25 | 04-25-2007 06:14 AM |
| Another Neutral/Ground/Bonding Question | michael5 | Electrical | 3 | 01-31-2007 12:38 AM |
| Electrical receptacle replacement question | sherlock | Electrical | 7 | 05-20-2005 04:33 PM |
| New fixture wiring question | Unregistered | Electrical | 1 | 02-22-2004 08:34 PM |