60 Amp Sub Panel - Electrical - DIY Chatroom Home Improvement Forum
Old 12-31-2007, 09:31 AM   #1
MsE
60 amp sub panel
Hi,
I am installing a sub panel off the main. I was advised by the electrician to buy 6/3 and 4/3 wire. the sub panel has a 2 pole 40 amp breaker and a single pole 20 amp breaker. I am connecting my double wall oven to this sub panel and running my appliances off the 20amp. i am assuming he is going to connect the wall oven to the 40 amp using the 4/3 wire and the 6/3 wire will be run from 2 pole 60amp breaker on the main panel to the sub. Am i right?
MsE is offline   Reply With Quote
Old 12-31-2007, 09:38 AM   #2
Master General ReEngineer
Bondo's Avatar
Rewards Points: 1,612
Ayuh,.......
Seeing that 4 gage is Bigger than 6 gage,.....
I believe you have it Backwards........
Bondo is online now   Reply With Quote
Old 12-31-2007, 09:43 AM   #3
MsE
60 Amp
so 4/3 from the main to the 60 amp and the 6/3 wire for the double oven to the 2 pole 40amp?
Old 12-31-2007, 09:48 AM   #4
Bondo's Avatar
Ayuh,.......
Bigger Wire carries a Bigger Current.......
The 4 gage will carry Both the Oven current,+ the appliances.......
The 6 gage will only be carrying the Oven current.....
Old 12-31-2007, 09:51 AM   #5
MsE
thank you so much! I have been very worried about doing this right.