#6 wire splice to #12 for dusk to dawn
Couldn't come up with a good title. But the previous homeowner had a garage in the back and later tore down. I found the underground cable which is 6 guage and wanted to install a dusk to dawn light without having to run new cable. At the light I spliced in to it with 12 gauge, back at the panel its setup for 240 on 50 amp breakers. Can I just remove the white/neutral and splice it with #12 and tie it in the neutral section? Should I just leave the #6 black on the 50 or should I splice it with #12 and run it in to a 20 amp breaker? Or is all this nuts? I wanted to avoid trenching new wire but if this is a big safety risk I will. Thanks in advanced, let me know if you need more info.
Be just as careful at the other end mounting your light and sensor. |
Was searching and found this http://www.diychatroom.com/f18/50-am...-12-3-a-62545/ , seems like I should do 12 on both ends?
Thanks Tarheel, didn't realize you had answered until I posted the 2nd time.
The suggestion is made to splice on a short length (a pigtail) of #12 gauge wire at the other end (in the panel) also, to remind a future owner or electrician that this is a 20 amp circuit.
A two conductor cable (black and white) can be for 240 volts or for 120 volts but not both. Even for 120 volts only you can put a subpanel at the garage location with 15 and 20 amp breakers for lights, etc., and keep the #6 line on the 50 amp breaker in the main panel. |
| All times are GMT -4. The time now is 10:00 PM. |