Originally Posted by Techy View Post
250.64
(B) Securing and Protection Against Physical Damage.
Where exposed, a grounding electrode conductor or its en-
closure shall be securely fastened to the surface on which it
is carried. Grounding electrode conductors shall be permit-
ted to be installed on or through framing members. A 4
AWG or larger copper or aluminum grounding electrode
conductor shall be protected if exposed to physical damage.
A 6 AWG grounding electrode conductor that is free from
exposure to physical damage shall be permitted to be run
along the surface of the building construction without metal
covering or protection if it is securely fastened to the con-
struction; otherwise, it shall be protected in rigid metal
conduit (RMC), intermediate metal conduit (IMC), rigid
polyvinyl chloride conduit (PVC), reinforced thermosetting
resin conduit (RTRC), electrical metallic tubing (EMT), or
cable armor. Grounding electrode conductors smaller than 6
AWG shall be protected in RMC, IMC, PVC, RTRC, EMT,
or cable armor.
stevekem is offline   Reply With Quote
Old 10-08-2012, 07:42 PM   #62
Master Electrician
you've got to clip it nice and neat or else it won't pass inspection. Best to call your inspector and have them tell you what they want to see. The do make clips to fasten the wire. any electric supply should carry them.
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
Old 10-08-2012, 11:03 PM   #63
Thanks again... Last question for now..
I'm thinking of having a switch inside house to turn outside garage lights on/off. I was going to run (3) #12 THWN for the switched hot and ground in the main conduit with feeders. Do I need to bring in a neutral as well for the switch?
Old 10-08-2012, 11:49 PM   #64
Master Electrician
You need a neutral at the switch location. As for running the branch with feeders that's a whole other arguement.
Resistor/Led and Basic Electricity Questions Khivar Electrical 19 04-16-2012 07:15 PM
efficiency voltage drop wire gauge jackwashere Electrical 6 02-18-2012 09:33 PM
Wire, Conduit and Voltage Drop Questions kikdrum Electrical 9 03-01-2009 07:50 AM
Replacement Meter Panel leonard_voet Electrical 19 04-09-2008 11:27 AM
Voltage Drop Manuel6 Electrical 1 01-16-2007 06:20 PM