6% Voltage Drop For 60 Amp Sub Panel? - Electrical - DIY Chatroom Home Improvement Forum
Old 08-15-2012, 03:46 PM   #1
Rewards Points: 184
6% voltage drop for 60 amp sub panel?
Hello,
I am planning on installing a 60 amp sub panel in my detached garage. Originally I was going to run (3) #6 THWN feeders with a #8 ground, buried in conduit. The total distance from main panel to sub panel is about 160 feet.
After using a voltage drop calculator at southwire, it is saying my voltage drop is going to be 6%+ using this wire.
1) At what percent of voltage drop should I try to stay under?
2) Southwire calc is recommending #2 THWN or #2/0 Aluminum for my feeder, does this sound about right?
Thanks for the help!
stevekem is offline   Reply With Quote
Old 08-15-2012, 03:51 PM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,878
Depends on your calculated load.
If you figure a calculated load of 48A I come up with #4cu.
Old 08-15-2012, 04:01 PM   #3
Rewards Points: 184
Thanks Speedy... Right now, I'm only planning on using overhead lights and a space heater. This will be used for storage of products for my home based business. When I finally decide to use it as regular garage, I will have more load from the typical tools such as a table saw, compressor, etc... I'm not real sure what calculated load I should be going for. Any thoughts?
Old 08-15-2012, 04:02 PM   #4
Rewards Points: 184
If this was your garage, what size wire would you run?
Old 08-15-2012, 04:03 PM   #5
Master Electrician
2 seems awfull big
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
Old 08-15-2012, 04:09 PM   #6
Rewards Points: 184
Andrew79, that's what I thought too... I'm trying to avoid going up to #4 THWN if possible because of price, but if that's what is needed then I guess I have to...
Old 08-15-2012, 04:15 PM   #7
Master Electrician
Speedy's most likely right with the number 4 I would think. Still smaller than 2 so should save you some coin.
It depends on your heater. You can really only have one or two tools running at the same time so the wattage of your heater will determine your service size for the most part.
Old 08-15-2012, 04:18 PM   #8
Rewards Points: 184
Garage is only 300 sq ft, not sure if that affects anything... I guess I could drop my breaker size down to 40 amp, but not sure if that would be enough in the future or not?
Old 08-15-2012, 04:21 PM   #9
Rewards Points: 184
Which do you think would be the cheaper route to go, #4 THWN or #2/0 aluminum? Any drawbacks to going with #2/0?
Old 08-15-2012, 04:41 PM   #10
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Drawbacks:
1) 2" PVC
2) 60A breaker not rated for 2/0 connections.
Old 08-15-2012, 05:00 PM   #11
Rewards Points: 184
I just priced the 2/0 (w/ground) and it's much cheaper than the copper... I think I will go this route. At 160 ft, what size breaker should I go with that is rated for 2/0 connections?
Old 08-15-2012, 05:01 PM   #12
k_buz's Avatar
2/0 AL XHHW is cheaper than #4 THHN/THWN? Don't believe it.
The Following 2 Users Say Thank You to k_buz For This Useful Post:
frenchelectrican (09-02-2012), Speedy Petey (08-15-2012)
Old 08-15-2012, 05:02 PM   #13
Rewards Points: 184
Just to clarify my question, at what breaker size should I go with (that is rated for 2/0 connections) that will keep my voltage drop at an acceptable level?
Old 08-15-2012, 05:03 PM   #14
Rewards Points: 184
At HD, price was only $1.42/ft for 2/0 with ground. #4 THWN was more than double that. Am I pricing the wrong wire?
Old 08-15-2012, 05:05 PM   #15
Rewards Points: 184
I am pricing 2-2-2-4 SE cable at $1.42/ft
Resistor/Led and Basic Electricity Questions Khivar Electrical 19 04-16-2012 07:15 PM
efficiency voltage drop wire gauge jackwashere Electrical 6 02-18-2012 09:33 PM
Wire, Conduit and Voltage Drop Questions kikdrum Electrical 9 03-01-2009 07:50 AM
Replacement Meter Panel leonard_voet Electrical 19 04-09-2008 11:27 AM
Voltage Drop Manuel6 Electrical 1 01-16-2007 06:20 PM