#6 Or #8 AWG For 50 Amp / 240v - Electrical - DIY Chatroom Home Improvement Forum
Old 04-21-2011, 07:08 PM   #1
#6 or #8 AWG for 50 amp / 240v
I'm installing a spa and it requires 50 amps /240 v. My run from the panel to the interruptor is 70' (approx.). Will #8 ga. wire suffice or do I need to upgrade to #6?
mmacnz is offline   Reply With Quote
Old 04-21-2011, 08:09 PM   #2
dSilanskas's Avatar
dSilanskas is offline   Reply With Quote
Old 04-21-2011, 10:13 PM   #3
Missouri Bound's Avatar
Although # 8 is adequate for a 50 amp circuit, you need to consider the length of the run. As dSilanskas states, you will need #6 at that distance.
Old 04-21-2011, 11:51 PM   #4
" Euro " electrician
frenchelectrican's Avatar
Go with 16mm˛ { #6 AWG } that will handle fine for that distance however there is the other item may get your attetion is the type of cable if you going to bury it from the house to the spa panel or interruptor panel and I Know in USA you can not have bare grounding conductor but not sure if the Canada do follow it. { I know France the SWA is allowed but couple other cable is limited unless it run in conduit then use THHN/THWN conductors this is the only legit way }
So please state your location if you are in USA or Canada so we can able post the correct regulations to follow it.
Merci,
Marc
Old 04-23-2011, 08:12 AM   #5
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,974
#8cu is only good for 50A if it is conductors in conduit or MC cable. #8NM is only good for 40A.
Replacing 240V Wall Heater with 240V Base Board Heater jasoncw Electrical 7 11-26-2010 10:39 AM
Halide High Bay Wiring 240v MarsHangar Electrical 1 08-11-2010 11:06 AM
Wiring two 240v appliances to one circuit brandykn Electrical 2 02-02-2010 09:44 PM
New 240V receptacle reads zero volts Madroaster Electrical 32 09-19-2009 12:35 PM
Do you think a tool running at 240v works better than at 120v? Piedmont Electrical 39 07-03-2009 09:50 PM