Old 03-08-2011, 07:55 PM   #1
50 Amp RV Receptacle, 100' run
I need to install a 50 amp RV receptacle on the far wall of my shop building. The run will be all inside from a 200 amp panelboard going up 8' in conduit, then a 82' run without conduit on top of a purlin, then 10' down in conduit to the receptacle. I believe that to keep the voltage drop reasonable I can use 6 awg. Keep in mind that a 50 amp RV service uses the two legs as separate 120's and does not use 240. What cable can I use for this? Or do I need to use separate conductors in EMT for the whole run? Thanks
Roaddoggie is offline   Reply With Quote
Old 03-08-2011, 08:11 PM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Even if there are no 240v loads (which I doubt) it is still a 120/240v circuit.
I would use #6THHN conductors in conduit myself. Two hots, neutral and ground. You can drop to a #10 for the ground.
Old 03-08-2011, 08:48 PM   #3
Actually, you're right, there are supposely some top end buses that use 240, but most RV's don't. I know my diesel pusher doesn't. And what would be cheaper, SER or separate conductors in EMT?
Old 03-08-2011, 09:03 PM   #4
Cheaper?
Probably #6 NMD on surface sleeved in conduit as you mention since you can get it cut easily from a wholesaler. The cleanest and "best" would be to have THHN all in conduit... but it's up to you.
Nobody runs 60A hot tub loads with THHN in conduit in practice, but in a large shop where you are moving things and using tools I would like to protect it everywhere, if you're covering it in wall with drywall, it could be NMD with probe plates and as long as the run is high, it would meet code in my area.
cschwehr is offline   Reply With Quote
Old 03-08-2011, 09:05 PM   #5
I mean sleeved in PVC till you get above 8'... Not the whole run.
Old 03-08-2011, 09:15 PM   #6
#6 thwn
Tigerloose is offline   Reply With Quote
Old 03-08-2011, 09:19 PM   #7
Originally Posted by Tigerloose
#6 thwn
Why? It's all indoor, he doesn't require a wet location rated cable...
Old 03-08-2011, 10:10 PM   #8
THWN is a conductor, not a cable. And when was the lat time you got THHN that was not dual rated with THWN?
Old 03-08-2011, 11:43 PM   #9
One minute you're making sure sure I'm correct on my terminology and the next you're telling me that it's always dual rated - you're correct on both topics though... Thanks for ensuring my initial posts are slowly typed in the future or not typed at all.
Old 03-09-2011, 05:28 AM   #10
Hey, no problem.
Switched Receptacle Question MrBill_DIY Electrical 3 11-21-2010 11:07 PM
Welder Receptacle - What Electrical Box SNAFU Electrical 4 10-26-2010 10:45 PM
Wiring A Ceiling Fan, Receptacle, and Outside Light merlin6984 Electrical 9 03-26-2009 10:52 PM
Receptacle Rating question KE2KB Electrical 19 12-20-2008 07:20 PM
Split Receptacle on 3-Way Circuit NPS Electrical 6 11-03-2005 10:28 AM