50 Amp RV Outlet - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 05-22-2011, 11:16 AM   #16
Rewards Points: 1,016
Originally Posted by Speedy Petey View Post
Yes. Sink a ground rod (not that it will do any good).
OP does not specifically say this is detached from shop building, if not no need for a ground rod, if detached then yes a ground rod is needed.
Old 05-22-2011, 11:27 AM   #17
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,034
He says it is 100 feet from the panel.
"I'm installing a 50 amp-4 wire 120/240 volt RV outlet about 100' from the panel in my shop. I have two main questions."
So I assumed that it is remote from the building but I guess it could be a very large building.
Interesting issue though:
If the RV box is mounted on the outside of the building , no ground rod required. If you put it on a post a foot away from the building, a ground rod would be required
Coastal South Carolina
rjniles is offline   Reply With Quote
The Following User Says Thank You to rjniles For This Useful Post:
Speedy Petey (05-22-2011)
Old 05-22-2011, 01:16 PM   #18
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,822
I'm with rjniles. I think it is a safe assumption since it is 100' away.
If not then that is one big a** shop.
Old 05-22-2011, 01:30 PM   #19
Agreed, I think it's also detached - due to the distance comment and desire for conduit. But it could be a large workshop, metal out-building, farm building, etc. So thought I would point it out for completeness.
Old 05-22-2011, 02:13 PM   #20
Scared Electrician
Saturday Cowboy's Avatar
Originally Posted by powerfactor View Post
Cowboy
How do you feel about this?
551.73
(D) Feeder-Circuit Capacity.
Recreational vehicle site
feeder-circuit conductors shall have an ampacity not less
than the loads supplied and shall be rated not less than
30 amperes. The neutral conductors shall have an ampacity
not less than the ungrounded conductors.
Thank You
Ragged Trousered Philanthropist
Please follow the code - its there for your safety no matter how inconvenient.
Saturday Cowboy is offline   Reply With Quote
Tags
rv outlet
Switched Outlet Issue mjm Electrical 13 06-14-2015 08:56 PM
Changing Two Gang Outlet to Three Gang Outlet vbullinger Electrical 9 01-10-2011 06:13 PM
Wiring a GFCI Outdoor Outlet from an Inside Outlet - Parallel or Series? Pacal Electrical 28 11-13-2010 04:36 PM
Outlet before light switch; Open Neutral? Fox Electrical 21 09-26-2010 09:38 PM
Just for fun Andy in ATL Electrical 56 10-20-2009 10:33 AM