As there is nothing to assure that every other circuit is turned off I feel it would be prudent to count the neutral as a CCC. In this case the reduced ampacity would apply.
If you turned off every other circuit, you would still only have TWO current carrying conductors... They would just be Line to neutral, not Line to Line.


stickboy1375 is online now   Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas line near branch load center pyroarchy Electrical 6 03-03-2012 06:41 AM
Can you drill Load Center? Ralph III Electrical 18 02-24-2012 12:24 PM
Whole house surge protection, help.... Ralph III Electrical 59 01-31-2012 12:37 PM
Main box feeding 220v and 110v brearker box off a 50am breaker? uvamosk Electrical 30 10-14-2009 10:46 PM
Load center vs. bottom fed Panel Board. Ugh. wmldwilly Electrical 8 04-23-2009 07:48 PM




Top of Page | View New Posts

Copyright © 2003-2014 Escalate Media. All Rights Reserved.