My intention is to connect a 4 prong plug into a 50a 220v box at festivals.
The line will be run from the 50a 220v to a concessions trailer using 8/3 SOW with ground.
At the trailer the 8/3 SOW with ground will run into a 2 pole 40 amp breaker.
The 40 amp 2 pole breaker will run to a 110/220v 100 amp load center.
The load center has 6 circuit breakers on two separate poles (20,15,15 and 20,15,15) that will run 12/2 to the outlets. All breakers will run 110. The two poles will not be bridged. Breaker usage: 1) 1500 w 2) 1800 w 3) 252 w 4) 515 w 5) 28 w 6) 194 w.
I am ASSuming that my breakers will not allow me to draw more than 40 amps through the incoming power line even though the festival connection is able to supply 50 amps.
A neutral conductor that carries only the unbalanced current from other conductors of the same circuit shall not be required to meet the requirement of a current-carrying conductor.
As there is nothing to assure that every other circuit is turned off I feel it would be prudent to count the neutral as a CCC. In this case the reduced ampacity would apply.
The atmosphere you are describing inclines me to believe that the general public will be around this setup? If that is the case, no way you can do this.
You need a license, insurance, permits.... DIY work is only for your OWN property, basically, the law doesn't care if you hurt or kill yourself doing your own stuff on your own house, but when the general public is involved, it's a whole different ball game.
What if someone is hurt or killed, are you going to be able to live with that?
The concession trailer is my own property and a certified electrician checks my wiring and the makes the final connection to the supply. If connections I have not made are unsafe no connection to power is allowed. It is not uncommon for concessionaires to do their own work then get approved by the cert electrician at the event. It is an industry standard. In fact, most of us do plumbing, construction, wiring, accounting, marketing, sales, contract negotiation, painting, signage, design, etc. The health department, building inspectors, and electricians are there to make sure nothing is unsafe. I have full confidence that no one will ever be exposed to unsafe conditions at an event. To date I have never heard of a single electric problem at an event.
I am looking for a straight forward answer as to whether my proposed set up will work or not, if you cannot provide me with the requested information then please refrain from further comments.
I am here asking people for opinions. The certified electrician at my next event will do a final approval. Unfortunately, his services are unavailable to me until then.
I have been told by my local electric supply company that this will work. However, I would never move forward without a second and perhaps third opinion. It is my experience that not every answer a person receives is accurate. Just as all certified electricians are not the same grade.
I just (quickly) looked over art 525 and the only thing that might be an issue is how you connect to power and the amps city of #8 SOW. You may be required to connect to power via a receptacle instead of hard wiring to a breaker.
8/3 SOW is only rated for 35a. Since 35a is considered a common breaker size, you couldn't fuse it at 40a.
Its a 50amp 220 box at fairground to 8/3 grounded to my trailer where is goes to 40 amp main then individual breakers. 8/3 is rated for 40 amp. I have provided my draw which totals @35 amps. Maybe I am not understanding what you said?
Stop yelling. It's not Jim's fault you didn't know that the appropriate term was 8/4.
As for your reply to my post, the issue here is not whatever your actual load may be. The issue is that you can't protect 8/4 SO with a 40A breaker, you need a 35A.
The 50 amp female box is an inlet for the male plug. Am I right about that? Any other issues with the diagram?
Refer to RV wiring to campsites. Keep in mind that campsites provide 30a 110 or 50a 110....thats a difference. But the lead power cord between rv and campsite is the same.
You are right. Just had a honda manufacturing electrician look at it. The male into box needs to be female and the box needs to be male. Also.....would be better to run 30 amp main and be well under for the 100 foot run. Thank you.
I have been thinking about this whole neutral as a CCC thing and one thing that wasn't mentioned was that in your OP you are stating the voltage as xxx/220, but I don't remember seeing of it was three phase or single phase.
It is not clear which you actually have, but a three phase service doesnt seem out of the question for this type of setting. If it is a three phase service, you will have to count the neutral as a CCC when using 8/3 W/ground SOW.
Thank you everyone. I will be uploading the corrected diagram (fingers crossed) ...let me know.