5 Gang Box Wire Size And Cu? - Electrical - DIY Chatroom Home Improvement Forum
Old 10-12-2012, 11:13 PM   #1
Rewards Points: 33
5 gang box wire size and cu?
I have 5 switches that i need to install. Looking at getting a 5 gang box. This will be installed in a 2x4 wall. What code is there about how many wires can be in the box? I plan on using 12/2 wire. There will be 2 circuits. 2 switches on one circuit and 3 switches on another circuit. Can i do this or do i need split out the boxes?
jgrohol is offline   Reply With Quote
Old 10-12-2012, 11:15 PM   #2
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
You should be fine. To be sure we would need to know the dimensions of the box. You can have multiple circuits in the same box.
Old 10-12-2012, 11:17 PM   #3
Rewards Points: 33
I thought so. Its all about the cubic in of the box? Any sizing i should be aware of?
Old 10-12-2012, 11:21 PM   #4
Electrical Contractor
jbfan's Avatar
Rewards Points: 152
I came up with 56.25 cu with your cable and devices, so anything larger will be fine.
Last edited by jbfan; 10-12-2012 at 11:41 PM. Reason: Math error and another math error, or maybe a drinking error
Old 10-12-2012, 11:26 PM   #5
k_buz's Avatar
Correct.
Add up all the current carrying conductors and multiply that number by 2.5, then add 2.5 to that answer to account for the grounds. Next you have to account for the devices themselves. Each device counts as two CCC's, so that's 25 cubic inches. Add that to the running tab.
So, if you have 2 12/2s feeding the 5 gang and 5 12/2s for the switch legs you get a total of 62.5 cubic inches.
I am estimating here, the dimentions of a 5 gang is 3x8x3=72 cubic inches.
Old 10-12-2012, 11:31 PM   #6
Rewards Points: 33
As always you guys rock. Thanks for the info.
Old 10-12-2012, 11:33 PM   #7
Rewards Points: 33
And the pigtails between switches don't count toward the needed CU right?
Old 10-12-2012, 11:36 PM   #8
k_buz's Avatar
Nope, only conductors that enter or exit the box.
Old 10-12-2012, 11:36 PM   #9
Originally Posted by k_buz View Post
Correct.
I came up with 56.25. 12awg is 2.25 in^3. Either way there is still room.
Sliver is offline   Reply With Quote
Old 10-12-2012, 11:38 PM   #10
k_buz's Avatar
My bad, you are correct, I didn't look at my code book and for some reason was thinking 2.5 for a #12...my bad.
What size ground wire should I use for 8 gauge power dxmullin Electrical 1 07-06-2011 03:57 PM
Wire size to 100 AMP subpanel Coqui Electrical 22 06-19-2011 07:28 PM
wire size for 160' feeder to subpanel steveski Electrical 3 05-21-2011 10:41 AM
Wire size for dryer jamiedolan Electrical 14 01-15-2009 06:43 AM
wire size wire to 10kw furnace? lochcarron Electrical 1 04-10-2005 08:43 PM