macp123 04-06-2012 02:10 AM
I am doing a service upgrade from 200 Amp to a 400 Amp service. The existing service is an all in one 200 Amp metered service panel. The plan is to install a new 320/400 Amp socket meter and install a second 200 Amp panel.
My question is, am I able to remove the meter from the existing 200 Amp panel and still use it with the new service by placing a meter cover socket blank on the meter socket? If I am able to re-use the existing panel is there anything else I should be aware of?
Thanks in advance.
Mark
kbsparky 04-06-2012 02:47 AM
Most CSED boxes can NOT be used as a sub-panel, since the neutral is permanently bonded to the can.
You may have to change it to a regular load center, or install a separate isolated neutral bar assembly.....
macp123 04-06-2012 07:57 AM
When you say I may have to change it to a regular load center, what exactly do you mean? How would someone go about doing it code wise?
shockme123 04-06-2012 09:08 AM
up-grade service
no- not unless panel is rated for 400 amps ? :eek:
k_buz 04-06-2012 09:16 AM
Why would the panel need to be rated for 400A? It would be protected by its own OCPD.
kbsparky 04-06-2012 12:40 PM
THis means you remove the existing meter/panel combo, throw it away, and then install a new regular panel in its place .... :whistling2:
Speedy Petey 04-06-2012 02:04 PM