40 Amp On 30amp Circuit - Electrical - DIY Chatroom Home Improvement Forum
Old 01-16-2010, 06:51 PM   #1
40 amp on 30amp circuit
I thought this was electrical not for appliance.
I have a friend who is buying a new wall oven to replace her old. Frigedaire Gallery 27" single electric. model FGEW2745KF
She asked me if I would like to do the change out since she wants to raise the new oven up in the existing cabinet so as not to have to bend so far. I can relate to that part.I was on board
The specs I originaly heard and saw called for a 40amp circuit, her current oven is on a 30amp breaker. Told her I would'nt be wiring this if this was the situation and she agrees wishing to be safe with her new oven. She has an electrician, so I asked her to have him check the panel to confirm that the wire on the 30amp breaker could not carry a 40amp load.
Bottom line it's a 30amp circuit. The store is telling her it won't pull even 20amps running so I had her send me the specs on it. amps17/15,connected load 4.1kw @240.
so why call out a 40amp breaker with these specs, will the 30amp carry?
she's a good friend and I would like to know she is safe. Is this just store confusion, wrong original specs attached to same oven model?
appreciate the help thaks timothy
Old 01-16-2010, 07:07 PM   #2
Where did these "specs" come from?
What does it say in the installation instructions for the range?
Try this...
http://manuals.frigidaire.com/prodin.../318201532.pdf
And this...
http://www.frigidaire.com/products/k...ens/fgew2745kf
Billy_Bob is offline   Reply With Quote
Old 01-16-2010, 07:07 PM   #3
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,974
There has to be some mistake in the instructions. There would NO valid reason to require a 40A circuit for a 4.1kW maximum load.
Old 01-16-2010, 07:09 PM   #4
Link with info on oven...make sure its the right model
Check the nameplate on it, possibly the wrong manual was included
Connected Load (kW Rating) @ 240 / 208 Volts = 4.1 / 3.0 kW
Amps @ 240 / 208 Volts = 17.0 / 15.0 Amps
Recommended Circuit Breaker – 20 Amps
Link to PDF:
According to their Spec/Installation Manual a 20a should work
Appliance...............Protection
Rating Watts.........Circuit
240V......................Recommended
Less than 4800W...... 20A
4800W - 7200W........ 30A
7200W - 9600W........ 40A
9600W and +............. 50A
Old 01-16-2010, 07:10 PM   #5
Thanks Bob.
Tpolk, you got your specs wrong. That unit requires a 20 amp circuit.
Last edited by Speedy Petey; 01-16-2010 at 07:10 PM. Reason: Oops. Dave beat me to it.
Old 01-16-2010, 07:13 PM   #6
the first set of specs she handed me had her oven and called ou 49amps, sounds like there was confusion somewhere because they were a printed out complete set with her model. second set she emailed to me thru adobe gives the info I show . thanks I feel better now
Old 01-16-2010, 07:14 PM   #7
i will check oven and specs when it shows up just to be sure
Old 01-16-2010, 07:39 PM   #8
Good! Get it straight from the horse I say (manufacturer, manufacturer's specs/installation instructions, etc.).
Need a wiring diagram Mooreski Electrical 47 02-01-2015 03:07 PM
Tripping breakers,neutrals,120 volts and 240 volts OH My!!! Stubbie Electrical 17 06-11-2011 06:09 AM
Changing a 3 way circuit...using recessed lighting box as a junction box? Oxymoron Electrical 1 12-07-2009 06:46 PM
Wiring a single pole switch into a 220v circuit rlmorgan Electrical 38 10-15-2008 07:59 PM
So lost - electrical requirements please help lapsis9 HVAC 4 12-20-2006 08:09 PM