4 Prong Dryer Outlet & Breaker Installation - Electrical - DIY Chatroom Home Improvement Forum
Old 03-29-2012, 06:11 PM   #1
This is my first time using a four prong appliance. I had no problem switching out the breaker for a 50 AMP (I know its overkill but we had one sitting around) and put up some heavy gauge copper in the basement. When I attached the wires to the breaker box I noticed that some ground wires were also attached to the same bar as the neutral (white) wire. When I looked at the instructions for the outlet it called the neutral (white) a "service ground" and the normal ground (green) "Earth Ground" or something like that...
so now for my question... I decided to put the ground (green) and neutral (white) on the ground bar. Is this terribly wrong or am I supposed to put the neutral (white) on the neutral bar??
... and what the heck... here's a diagram...
flipjarg is offline   Reply With Quote
Old 03-29-2012, 06:19 PM   #2
Pure Genius
Rewards Points: 150
As long as the panel is the first means of disconnect for your service then you are ok. Why a 50 amp for a dryer and by heavy gauge copper what size do you mean?
Dierte is offline   Reply With Quote
Old 03-29-2012, 06:20 PM   #3
Electrical Contractor
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
What will you be running on this circuit and what size wire are you using?
With Electricity there is the right way to do it and the dead way. Just because it works does not make it safe.
rrolleston is offline   Reply With Quote
Old 03-29-2012, 06:21 PM   #4
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
You can't have a dryer on a 50A circuit. It would have to be 30A.
Old 03-29-2012, 06:24 PM   #5
Originally Posted by Dierte View Post
Why a 50 amp for a drye...
We just had one there at the time and decided to use that instead of buying a new one.
The only thing running on this circuit is the dryer. I shouldn't have said heavy... it is only 10 gauge.
Even if we are only running a dryer on it and that's it? We will never be running anything else on it.
Old 03-29-2012, 06:25 PM   #6
k_buz's Avatar
Also, to switch over from a 3 wire to 4 wire recept properly you have to remove the bonding strap in the dryers wiring compartment.
Old 03-29-2012, 06:28 PM   #7
k_buz's Avatar
To properly protect the dryer is has to be on a 30 A circuit.
Old 03-29-2012, 06:30 PM   #8
Are you talking about if I switched the plug-in on the dryer from 3 to 4 prong? We purchased the dryer with a 4 prong plug-in already installed.
Old 03-29-2012, 06:32 PM   #9
k_buz's Avatar
10 AWG is only rated for 30 amps...not 50.
To properly protect the dryer, it must be on a 30 amp breaker
Old 03-29-2012, 06:34 PM   #10
k_buz's Avatar
I have wired many a dryer where the preinstalled 4 wire cord was improperly installed.
Old 03-29-2012, 06:36 PM   #11
Thank you for the info. I just watched the video on this page (http://electronics.howstuffworks.com...it-breaker.htm) and what you are saying makes total sense. I will take inside the wiring compartment in the dryer just to be sure.
Old 03-29-2012, 06:36 PM   #12
rrolleston's Avatar
Unless this is a 50 amp dryer with 50 amp receptacle and cord with #6 copper wire it could be really dangerous and you should replace the breaker with a 30 amp breaker.
Also did you have a 4 wire feed where the dryer receptacle is?
If the panel has a separate neutral and ground bar for example in a sub panel they must remain separate.
Old 03-29-2012, 06:42 PM   #13
Thanks for the input... its nice to see two people agree. I will definitely switch the breaker to a 30amp. There was no dryer in this spot before so I wired the receptacle/outlet.
So... from what I have learned from this thread... the new picture (attached) is correct.... right?
Old 03-29-2012, 07:10 PM   #14
jbfan's Avatar
Rewards Points: 478
The breaker is in place to protect the wiring, not the dryer!
jbfan is online now   Reply With Quote
Old 03-29-2012, 07:11 PM   #15
jbfan's Avatar
Rewards Points: 478
That is correct.
Make sure that the bonding strap is disconnected from the neutral inside the dryer, like k_buz mentioned above.
Tags
4 prong , dryer , ground
Dryer - 4 prong to 3 prong majorwest Electrical 15 02-06-2012 05:03 AM
Odd voltages at outlet TJF Electrical 12 11-01-2011 09:13 PM
New electric dryer install trips breaker cortell Electrical 8 08-29-2011 09:09 PM
Circuit Breaker trips when I plug into an outlet Alex in Orlando Electrical 3 09-05-2010 01:04 AM
New electric dryer is blowing breaker! minameismud Electrical 7 09-14-2008 10:45 PM