-   -   4 gang box (http://www.diychatroom.com/f18/4-gang-box-170825/)
kosovofalcon 02-02-2013 12:19 PM
4 gang box
Ok, I want to wire a 4 gang box with 4 receptacles which will give me 8 plugs inside the box. I hope I explained that right. 2 plugs on each receptacles. It is on a 20amp circuit it is at the end of the ciruit and it will have one circuit wire entering the gang box. Do I have to pigtail 4 black wires going to brass connectors and 4 white wires going to silver connectors to each recpetacle. and 4 ground wire to each one as well. When doing the pigtail does it matter if the black and white pigtails go to the same level on the receptacle or does the black need to go to the top brass screw and the white go to the ssilver screw on the bottom. I hope this is making sense. Thanks for your help
Daniel Holzman 02-02-2013 12:36 PM
You can wire the receptacles using pigtails, or you can connect the hot from the first receptacle to the hot for the second receptacle, then from the second receptacle to the third etc. Same with the neutral. Each outlet must be grounded, you can pigtail all the grounds together. If you use a metal box, you need to ground the box as well.
kosovofalcon 02-02-2013 12:51 PM
Does it matter top or bottom screw when connecting pigtails
herdfan 02-02-2013 03:21 PM
Not as long as you don't break off the tabs.
jbfan 02-02-2013 03:23 PM
No.
The grounds have to be pigtailed, they can not loop from receptacle to receptacle.
insaneirish 02-02-2013 04:20 PM
Not saying you're wrong here, but can you cite the code for this? I was trying to find it on my own and was unable to.
TarheelTerp 02-02-2013 04:27 PM
NEC 110.14 Wiring Methods conductors and screw terminal Only one conductor shall be installed under a terminal screw. In boxes with more than one ground wire, the ground wires shall be spliced with a wire tail or pig tail attached to the grounding terminal screw of the device.
brric 02-02-2013 04:33 PM
There is only ONE ground wire in the box, according to the OP.
kosovofalcon 02-02-2013 04:36 PM
Yes only one main ground coming in. I did pigtail the grounds and ground each plug . The black and white I do the same thing. Black to bronze and white to silver. When connecting black and white do they connect at the same level on the plug. Or does black go high and white go low.
insaneirish 02-02-2013 04:51 PM
Yea, does not sound like this is a prohibition against daisy chaining multiple outlets on the same EGC in a box. If there is something else that does prohibit it, I would like to know.
kosovofalcon 02-02-2013 04:58 PM
Ok thanks
k_buz 02-02-2013 05:09 PM
I've never been called on it and I do it all the time.
Kyle_in_rure 02-02-2013 05:12 PM
It does not matter, they can connect to either the bottom or top screw. Just make sure the black wire is always connected to a brass screw and the white wire to the silver screws.