4/0-4/0-2/0-#2 Legal For 200 Amp Sub Panel? - Electrical - DIY Chatroom Home Improvement Forum
Old 01-26-2012, 03:35 PM   #1
Electrical Contractor
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
4/0-4/0-2/0-#2 Legal for 200 amp sub panel?
Was at the electric supply checking on prices for wire and supplies and they said I should use 4/0-4/0-2/0-#2 wire for a 200 amp sub panel. Makes sense since my main disconnect is only 4/0-4/0-2/0 and I have to install a ground at the sub panel and seperate neutral and ground.
Any advice on this would be greatly appreciated.
rrolleston is offline   Reply With Quote
Old 01-26-2012, 04:43 PM   #2
MarginallyQualified
Rewards Points: 2,464
Will you be getting inspected?
Does your County/area require a 4wire (with ground) feed to sub panels?
ETA: I missed that this does have the 4th wire.
Is this THHN? or a URD quadplex?
Old 01-26-2012, 05:32 PM   #3
rrolleston's Avatar
Since I am in a neighborhood area an inspection will have to be done. The guy at electric supply even asked me why I would bother with a ground.
I was told by inspectors it's required and some come and say no. Thing about inspectors is they seem to have such a wide range of ideas. Friend worked all weekend on a hair salon when the inspector came he said fail you need cast drain iron drain pipes here. Another inspector said it was fine.
I have three wire now and it's just URD running in the attic to the panel not very safe but has been there for years. I would like to run conduit from the main panel all the way to the sub panel in my mobile home and run four wire to the panel.
I want to do this properly I am just getting so many mixed answers between people in the trade and people at some of the electric supply and AHJ. Called one electrical supply this afternoon and they said I had to run four 4/0 wires harder to pull and maybe larger conduit costing close to three times the price.
Old 01-26-2012, 05:37 PM   #4
rrolleston's Avatar
Also I may be able to reuse the wire that I have feeding the panel now. It's probably enough 4/0-4/0-2/0 just need to add a #2 wire and I think I have close to 100 feet of that somewhere.
I will have to measure if it's enough after I find out whether it's ok to reuse it. Does not look like anything wrong with it.
Old 01-26-2012, 08:45 PM   #5
I=E/R
a7ecorsair's Avatar
You never said if this sub will be in a building that is separate from the building that has the main or if it will be in the same structure as the main.
a7ecorsair is offline   Reply With Quote
Old 01-26-2012, 08:48 PM   #6
rrolleston's Avatar
Sorry yes it will be in a separate building
Old 01-26-2012, 10:00 PM   #7
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
I need a tad bit of clarification.
1.)Your service is for a mobile home
2.) Your service equipment (main disconnect) is on a pedestal or pole within 30 feet of the mobile home?
3.) The sub panel is 200 amps and it is in a separate building from the mobile home?
4.) Your wanting to feed that sub-panel from the service equipment enclosure where the main disconnect is located?
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 01-26-2012, 10:11 PM   #8
rrolleston's Avatar
Main service is in a garage but about 85 feet of cable length to the mobile home panel. Going to feed the sub panel with the feed through lugs to a sub panel with a main breaker and separate neutral and ground and will add two grounding rods and ground to copper water main.
All 200 amps
Old 01-26-2012, 10:15 PM   #9
UAW SKILLED TRADES
Stubbie's Avatar
All 200 amps
Sounds fine but why such a large sub-panel? Is the separate building a big shop or something?
Or are you just meeting the rules that the sub on feed thru must equal the service equipment rating?
Stubbie
Old 01-26-2012, 10:22 PM   #10
rrolleston's Avatar
We have an electric tankless water heater. And may possibly add an electric range in the future. The old panel was 150 amps fed by 4/0. Hoping after the conduit run they are still long enough.
Old 01-26-2012, 10:29 PM   #11
rrolleston's Avatar
Also currently our home is fed by two feeds from the main one 100amp main panel that was original to the home. And one feed to the 150 amp panel from the feed though lugs.
I really would like to feed the new 200 amp panel where everything in my home that runs on 220 will be connected. Then feed the 100 amp panel with the new 200 amp panel separating all the neutrals and grounds the way they should be and adding better grounding. And at the same time making everything underground
Old 01-26-2012, 10:34 PM   #12
UAW SKILLED TRADES
Stubbie's Avatar
So your running a new 4 wire main feeder from the service equipment in the garage to a new sub panel in the mobile home?
Stubbie
Old 01-26-2012, 10:37 PM   #13
rrolleston's Avatar
Yes. Main in garage is going to feed sub panel in the mobile home
Old 01-26-2012, 10:40 PM   #14
rrolleston's Avatar
Hate the idea of all wire being exposed and overhead with bonded neutrals in sub panels. Really want it done much neater.
Old 01-26-2012, 10:43 PM   #15
UAW SKILLED TRADES
Stubbie's Avatar
Ok, sorry it takes me awhile sometimes to get one the same page. I'd just buy some mobile home feeder
http://www.cable.alcan.com/CablePubl...eder+Cable.htm
You will need 4/0-4/0-2/0-4 aluminum. You do not need a #2 equipment
ground ...who told you that??
Everything else sounds good.
Stubbie
Garage Sub Panel Questions mscanlon01 Electrical 3 07-20-2011 10:03 AM
Extending Old Main Circuit Panel lkpowell Electrical 4 10-23-2008 02:15 PM
Replacement Meter Panel leonard_voet Electrical 19 04-09-2008 10:27 AM
Installing new (service?) breaker panel and generator panel Nhrafan Electrical 6 04-01-2008 03:03 PM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 07:37 AM