If you have a 320a meter, is it standard practice to put in two 200a panels? This is a house/big garage workshop and the panels will backup to the meter on the other side of the wall. The meter has double lugs so will two sets of wires be run to each panel with one set coming through the panel that has the conduit connection to the meter and on to the other? Or is there another way all this is done? Thanks in advance...
Roaddoggie is offline   Reply With Quote
Old 09-14-2009, 06:39 AM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 650
Seperate feeds. One to each panel from the meter, or disconnect outside.
jbfan is online now   Reply With Quote
Old 09-14-2009, 07:40 AM   #3
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,992
Like Jbfan said, one service entrance cable for each panel.
Typically one 350A riser up from the meter pan, or one lateral underground if that is how it is fed.
Old 09-14-2009, 10:47 AM   #4
Thanks, would it be typical to run six individual wires, USE, through what ever size conduit meets the 60% fill for a 8" long conduit into one panel and run three out through another conduit to the other panel mounted on the wall 16" to the side? Also, is the same rule of thumb in place for two 200a panels as for one when 2/0cu and 1awg is used?
Old 09-14-2009, 12:31 PM   #5
How do you know the amp rating of the meter?
I don't see it here
http://en.wikipedia.org/wiki/File:Electrical_meter.jpg
Old 09-14-2009, 12:49 PM   #6
I didn't see it on the meterbase (and the meter is not set yet), but that's what I paid for.
Old 09-14-2009, 04:36 PM   #7
jbfan's Avatar
Rewards Points: 650
The part of the panel will be very crowded with all the wires.
I would have seperate runs to each panel.
Without pictures, I can't really say how I think would be the best way.
Old 09-14-2009, 09:18 PM   #8
Definitely separate runs to the two panels.
Old 09-14-2009, 09:20 PM   #9
I don't see it here
What does it matter? He has a 320A meter pan that should be approved by his POCO. His end is done.
The meter itself has absolutely no bearing on it.
If the meter pan is wring then the whole thing is screwed up.
Old 09-14-2009, 09:23 PM   #10
" Euro " electrician
frenchelectrican's Avatar
It is my SOP for class 320 socket is run two seperated set of service conductors with two 200 amp panels useally far much cheaper than single 400 amp panel.
The only time I have to run true 400 amp panel useally on commercal location or farm one of the two.
Merci, Marc
Old 09-14-2009, 09:23 PM   #11
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
Yoyo, check this out. This is a 320 meter base. Notice the generous allowance of space for conductors.
http://www.ownerbuilderbook.com/imag.../full/4859.jpg
Old 09-15-2009, 09:15 AM   #12
This pic is exactly what I have. What I'm trying to figure out is the preferred way to run two separate sets of conductors as I need to final frame he inside wall for the panels. Would it be ok to come in through a knockout for one panel that backs up to the meterbase and then go out the bottom (like the pic) and into the wall and do two 90's to go up to the other panel?
Old 09-15-2009, 10:21 AM   #13
I was hoping to tell what service I have. I do not have a main breaker.
Old 09-15-2009, 11:29 AM   #14
Rewards Points: 246
As you can see in the picture, they used one conduit for two SE cables. That was not easy to do. What the others are encouraging you to do is to run 2 conduits. 1 for each 200 amp panel. You need one for the utility also. So consider where your conduits should go. In the back is a great place, especially if the two panels will be inside behind the meter. Try at all cost not to enter the top. You will need special fittings if you do, and it not a good practice anyway.
If it worked before you worked on it. You did something wrong.
Old 09-15-2009, 04:23 PM   #15
nap
You talking to me?
nap's Avatar
I don't see it here
not sure what you are after yoyizit. A meter base should have the ampacity marked on it somewhere but as they age, all bets are off as to finding any indication of what it is.
a somewhat dependable way to tell, at least in my area, is by the size and shape of the base.
round bases were generally 60 amp. small squarish were 100 amp and a bit taller rectangle is 200 amp. The 320 is a really good sized tin can.
I understand there were some round 100 amp bases but I have not run across any of them, personally.
and to having no main: that has been a requirement for a considerable time. If you do not have a main, then either your install is very very old (although I don't know how old it would have to be to not have a main disco. at least 60 years though I believe. not sure if no main was ever legally acceptable though), it was an illegal install when installed, or it was changed to an illegal installation.