3 Wire Connection For New Kitchen Stove - Electrical - DIY Chatroom Home Improvement Forum
Old 09-09-2007, 02:54 PM   #1
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,142
3 wire connection for new kitchen stove
I am changing out a drop-in kitchen range in a condo built in the early 1970's. Range is hard wired with a servive enterance cable type cable with 2 # 6 conductors and a twisted braid groud around the 2 conductors. This is wired to a 50 amp dual pole breaker with the braid connected to a common neutral ground buss. I realize that new installs require a 4 wire plug and receptacle but replacing this cable would be a bear. Can I install a 50 amp 3 wire receptacle on the cabe and a 3 wire pig tail on the stove and tie the neutral and the ground at the stove?
Old 09-09-2007, 07:07 PM   #2
Lic. Elect, Eng Contractr
lbwireman's Avatar
Short Answer: NO. In the event a fault should occur, an electrocuted family member or friend is also a "bear". See NEC 2005 Art. 250.24(A)(5) and Art. 250.142(B), unless the installation meets the requirements of Art. 250.142(B) Exception No. 1/Art 250.140. Note the use of the word "existing" and the references to other code articles. My advice to my guys has always been "err on the side of caution".
lbwireman is offline   Reply With Quote
Old 09-10-2007, 12:02 AM   #3
Maybe it would be helpful if you could attach the codes you are referring to, or post the links so we all can learn. Thanks
sluggermike is offline   Reply With Quote
Old 09-11-2007, 02:07 AM   #4
lbwireman's Avatar
Nec 2005
Available from NFPA. I gave you the citations, surely you can find a code book???? Try this
http://www.nfpa.org/freecodes/free_a...GpAf3QjTiH6vEJ
Select the entire URL (use yur R click button to "copy link address"), then put your cursor in the URL window of your browser, ctrl V, Enter. Do your homework. Enjoy.
Old 09-13-2007, 01:59 AM   #5
Rewards Points: 27
While I am not a fan of 3 wire supplies, see art. 250.140 2002 NEC,it is permitted in EXISTING installations to use a 3 wire supply. A feed with seperate grounded and grounding conductors is still the prefered method. If you make any changes such as moving locations of a receptacle,box then you would IMO, have to upgrade.
Norcal is offline   Reply With Quote
3 wire stove connection bgoldie Electrical 13 03-01-2011 01:29 PM
wire connection peteracki Electrical 6 05-18-2010 07:12 AM
Old house, new light fixture, too many wires Persephonee Electrical 3 01-15-2007 09:58 AM
got rid of kitchen island, how to get rid of the electrical wire from floor ckcrew Electrical 15 12-14-2006 10:45 AM
Three electricans said it was impossible! Tom Electrical 35 04-29-2006 06:06 PM