so i've decided to relocate and merge an electrical box. to make story short, i have a 3 way switch for the basement.
after some hands on research (existing wires), it seems that the previous owner had installed this configuration http://buildmyowncabin.com/electrical/img12.gif ![]() anyhow, i putz around.. and now switch 2 (the one away from the power source) can only be turned on and off while switch 1 (switch close to power source and light connection) is in the on position? WTF happened? i've tried numerous combos and now the wiring box looks like a total mess. please help.. one thing to note is that the previous owner placed the black and white cables in opposite positions as opposed to the diagram. |
#2 |
Can you post a pic of your current wiring (since it is now a "total mess")?
#3 |
Pedro, 1st, there is no "on" and "off" for a 3-way switch.
#4 |
Scared Electrician
you have a traveler and the switch leg crossed.
Ragged Trousered Philanthropist Please follow the code - its there for your safety no matter how inconvenient. |
#5 |
Electrician
Cowboy is right. Set it up exactly like the diagram and you'll be good.
Kyle Just because you can, doesn't always mean you should |
#6 |
Licensed electrician
The diagram will work, but technically shows a code violation of 200.7. The white can only be used as the feed to the switch.
Answers based on the National Electrical Code. Local amendments may apply. Check with your local building officials. |
#7 |
Your switches may have the terminals physically arranged differently. The common terminal is usually stained a darker color or has "C" engraved near it. If not you will need to look at the switch instructions, or use an ohmmeter (or continuity meter).
Or maybe you have a defective switch.
The average homeowner who lost his house in the Oklahoma tornadoes should move for good and not rebuild. Too much complexity watchdogging the contractor. Too much a chance to be defrauded. |
#8 | |
3 way switches. help me before i go insaneQuote:
can you be a little more clear which one is the traveler and which is the switch leg on the diagram listed above? thanks also what do you mean by "The white can only be used as the feed to the switch"?? tx |
#9 |
If you look at the drawing you will see one of the screws on each switch is black. That screw is the common screw. It is important that the black wire be on that screw for this diagram to work. You need to look at your switches to identify the common terminal. It may not be physically in the same position.
Do not PM with questions that can be asked in a forum. I will not respond. |
#10 |
I don't think it is a violation. The fixture has black and white wires connected to it. That code is made so that you don't have two white wires at the fixture.
#11 |
Electrical Contractor
At sw#1, the 2 black wires connected are the hot wires.
This feeds to sw#2, and connects to the common screw. The white and red of sw#2 are the travelers, and connect to the other screws. At sw#1 the black wire going to the light fixture is wires to the common screw to feed the light. The red and white are considered the travallers and connect to the remaining screws. The white wire from the breaker connects to the white wire going to the light. Your colors may vary. The common screw is a darker color, or marked with a C. Older switches are harder to tell.
Yes I am a Pirate, 200 years too late. "Jimmy Buffett" |
#12 |
Electrician
This help?
#13 |
Here is the section related to my post re white needing to feed switch.
(C) Circuits of 50 Volts or More. The use of insulation that is white or gray or that has three continuous white stripes for other than a grounded conductor for circuits of 50 volts or more shall be permitted only as in (1) through (3). (1) If part of a cable assembly and where the insulation is permanently reidentified to indicate its use as an ungrounded conductor, by painting or other effective means at its termination, and at each location where the conductor is visible and accessible. Identification shall encircle the insulation and shall be a color other than white, gray, or green. [ROP 5–26] (2) Where a cable assembly contains an insulated conductor for single-pole, 3-way or 4-way switch loops and the conductor with white or gray insulation or a marking of three continuous white stripes is used for the supply to the switch but not as a return conductor from the switch to the switched outlet. In these applications, the conductor with white or gray insulation or with three continuous white stripes shall be permanently reidenti fied to indicate its use by painting or other effective means at its terminations and at each location where the conductor is visible and accessible. Note that this section will not be needed since the 2011 will require a neutral at the switch location.
| The Following User Says Thank You to Jim Port For This Useful Post: | frenchelectrican (06-08-2011) |
#14 |
Electrician
On one hand, I agree, I personally would use a re-marked white to feed power to the switch. On the other hand, would it not be allowed, as the re-marked white in the diagram is not being used as a return to the switched outlet? Or would you consider sw 1 (the one with the source feed) to also be an ‘outlet’ as per NEC definition? Curious on your thoughts.
#15 |
I too can see that point Kyle. I use the white as the feed and keep the blk/rd as travellers for consistancy. I don't think I have ever asked an inspector for their take on this.
| The Following 2 Users Say Thank You to Jim Port For This Useful Post: | frenchelectrican (06-08-2011), SD515 (06-07-2011) |
| Display Modes | |
| 2 Lights & 3 switches, doesn't look right | curious1 | Electrical | 1 | 10-26-2010 11:26 PM |
| Question about wiring and voltage with switches and lights | rswurth | Electrical | 17 | 06-21-2010 12:12 AM |
| Question about switches on a 20 amp circuit | Abs777 | Electrical | 6 | 04-28-2010 11:09 AM |
| Replacing switches turning into nightmare. | RyanD | Electrical | 19 | 05-26-2009 07:19 PM |
| Need help replacing switches in four-way circuit | magnolia | Electrical | 3 | 05-09-2008 10:40 PM |