3-way switch wiring
Name:  3-way - power to switch.jpg
3-way switch wiring-3-way-power-light2.jpgI'm new to the site, and a certified electrician. I've been browsing the site and notice alot of people having trouble with 3-way switches. Here are some diagrams for quick reference. Maybe a sticky?
CheapCharlie is offline   Reply With Quote
Old 02-05-2011, 01:22 PM   #2
Licensed electrician
Rewards Points: 1,506
Before they get made into a sticky you might want to look at NEC 200.7. The re-identified white needs to the the feed to the switch.
Old 02-05-2011, 01:23 PM   #3
Rewards Points: 77
I'm from Canada. Must be different here
Old 02-05-2011, 02:06 PM   #4
Electrical Supplier
Rewards Points: 150
The New NEC requires a Neutral to be carried throughout the circuit on residential. I think they started this in 2008, I know it is in 2010....
Youll have to use 14/3 or 12/3 romex w/ground for between the switches and anywhere else where you need to.
no reidentifying anymore.....Red and Black are your travelers between the switches.
"Do it right the first time and avoid duplication of effort"
Your AHJ/Inspectors ALWAYS have the final say on ANY electrical code issue.
If in doubt, contact a licensed, experienced, reputable electrician to perform the work.
LyonsElecSupply is offline   Reply With Quote
Old 02-05-2011, 02:48 PM   #5
joed's Avatar
Rewards Points: 12,458
Nope the white needs to FEED the switch in Canada as well.
Old 02-05-2011, 03:47 PM   #6
Rewards Points: 83
This is the drawing that I give to new guys wiring up three way switches,
davido30093 is offline   Reply With Quote
Old 02-05-2011, 05:07 PM   #7
Rewards Points: 77
My bad, misunderstood what was being said earlier....BACK IN BLACK!
Old 02-05-2011, 06:35 PM   #8
Rewards Points: 506
According to my understanding, only the bottom image is non-compliant to the 2011 NEC. Correct?
jlmran is offline   Reply With Quote
Old 02-05-2011, 08:05 PM   #9
As I read it all are now none compliant with NEC 2011 which requires neutral to switch boxes. Or am I mistaken?
hayewe farm is offline   Reply With Quote
Old 02-05-2011, 08:09 PM   #10
Rewards Points: 506
I'm referencing 200.7(C). White conductors can be ungrounded in certain situations. Is there a citation which prohibits switch loops?
Also, what good is a neutral at a 3-way switch? It could work at the switch which receives the circuit feed, but it would serve no purpose to have a neutral at the other switch. Unless I'm blinded by ignorance.
Old 02-05-2011, 08:17 PM   #11
I believe the purpose to to have a neutral available for future upgrades to motion sensor or digital switches. I'm refering to NEC 2011 404.2(c)
404.2 Switch Connections.
(C) Switches Controlling Lighting. Switches controlling line-to-neutral lighting loads must have a neutral provided at the switch location.
Old 02-05-2011, 09:29 PM   #12
Rewards Points: 506
So, not including the exceptions provided, the only way to correctly (NEC 2011) wire a light circuit with 3-way switches is:
1. Power => switch => switch => light (Like davido30093 said above);
or
2. Use 4-wire cable in other configurations. Do these exist as a NM-type cable?
Is this correct?
Old 02-05-2011, 10:50 PM   #13
By the way all the drawings including #3 are NEC 2008 compliant. The re-designated white wires in drawing three are not used as a return which is the only restriction for their use as a re-designated wire.
Old 02-05-2011, 11:21 PM   #14
or
Is this correct?
Yes. or you could run 2 14-2 cables with one a redesignated white.
Beldon NM 4 cond comes in both -2/2 (example 14 2/2) an -4 (example 12 4) configurations. -2/2 is 2 pair of whit/black and the -4 is white black red blue.
Old 02-06-2011, 08:24 AM   #15
Rewards Points: 506
Last OP drawing: Why isn't the RD white wire in the right-side cable a return? Sure, it is feeding a 2nd switch 1st, but it still is returning the current to it's source after a switch.
Wiring an Intermatic Wall Timer in a three way switch aitutaki98 Electrical 6 07-23-2011 11:43 AM
Unusual three way switch wiring help r1racer Electrical 9 11-11-2010 08:49 PM
Switch on K&T wiring - OK to pigtail? fdmillion Electrical 4 01-27-2010 09:15 AM
Wiring two floodlights to a triple switch chrisjardine12 Electrical 20 01-23-2009 12:29 PM
Ceiling Fixture / Switch Wiring gregger Electrical 1 10-21-2006 07:47 PM