andrewmarcos@yahoo.co.uk 11-24-2008 05:41 AM
i recently purchased a commercial dishwasher that requires three phase power. I have a 4 pin point near the machine 3ph and earth (no neutral). The machine has five wires hanging out of it, 3ph, neatral and earth. how do i wire this up without the neutral?
Speedy Petey 11-24-2008 06:27 AM
I would imagine you do not. :no:
In the US you would have to run a new circuit; or in the extremely rare case of a full conduit run, pull a neutral in.
Gigs 11-24-2008 08:34 AM
Are you sure it's 3ph and not 1ph 220 with neutral and ground (also 4 pins?)
Wildie 11-24-2008 07:53 PM
Single phase may be required for solenoids, timers etc!
If so, you'll require a neutral. No easy way out of it!
nap 11-24-2008 09:36 PM
OP stated machine has 5 wires. That would mean 3 phase plus neutral plus ground.
frenchelectrican 11-25-2008 12:37 AM
Normally in the UK system the voltage are 230 L-N and 400~415v L-L { both single and three phase }
You should double check the nameplate to see what voltage it required and It will be wise go get the electrician come in and have it termated proeprly due the L-L voltage may knock ya out.
Merci,Marc
Gigs 11-25-2008 11:07 AM
I meant the outlet, not the machine.