3 Phase 3/4 Motor Switch - Electrical - DIY Chatroom Home Improvement Forum
Old 08-27-2012, 08:01 AM   #1
3 phase 3/4 motor switch
Hello! Could anyone point me in the direction of a suitable magnetic switch for a 3 phase 3/4 horse motor? All of the switches I've found are rated for a much large motor than the one I have. Could this be problematic? motor specs below.
THANKS!
MAGENETEK EXPLOSION PROOF
PH: 3
HP: 3/4
RPM: 1725
VOLTS: 208-230/460 (ITS ALREADY HOOKED UP TO 208/230, 30 AMP BREAKER)
AMPS: 2.8-3.0/1.5
HZ: 60
SF:1.0
TIME RATING: CONT
INS CLASS: B
AMB. C: 40
NEMA DESIGN: (BLANK)
CODE: K
gustonlemond is offline   Reply With Quote
Old 08-27-2012, 08:03 AM   #2
Master Electrician
Having a higher rating shouldn't hurt anything.
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
Old 08-27-2012, 08:10 AM   #3
Rewards Points: 13,450
Just to make sure you know if you plan on using this motor at your home, it's rare to even see 3 ph even avalible in a residential setting.
You would need a phase converter.
Homes are single phase.
Old 08-27-2012, 08:15 AM   #4
thanks, fortunately I have 3phase power in my building. It's already wired and running, I just need a switch. I'm turning it on and off via the breaker.
Old 08-27-2012, 08:49 AM   #5
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
You need one of these .... they also come 30 amp rated. Just go to an electrical supply or you might try e-bay to find one at less cost.
http://www.electricsupplyonline.com/...-1_w011453.php
http://www.ebay.com/itm/HUBBELL-30-A...item3f1b8b57b2
Old 08-27-2012, 11:45 PM   #6
" Euro " electrician
frenchelectrican's Avatar
There are couple issue that allready arise on this set up.,
First of all you do not need the 30 amp breaker that is way too big for this purpose you will need 15 amp three phase breaker that is the smallest one you can use on this size motour.
Keep in your mind that the 15 amp breaker is used for short circuit protection only and you will need a manual motour starter with overload relay or coil in there to fine tune protection on overload stuff and it don't take much to get them overloaded due you are running on three phase you may not notice the light flicker at all.
You can get new motor starter avce protection it will come in either IEC or NEMA frame size with eclosed box otherwise you can ask some of the electrical contractor to see if they have some on hand they can sell it to you.
Merci,
Marc
Tags
3 phase , motor , switch
hELP! Amperage needed for 220V motors 1488rob Electrical 36 01-28-2014 04:44 PM
Three phase transformer question rongaudier Electrical 8 03-08-2011 07:19 AM
Wiring Single Phase through 3 Phase socket tonyr417 Electrical 10 10-26-2010 09:09 PM
Want to add a single phase Subpanel to three Phase Main meglomachinist Electrical 19 09-10-2009 03:46 PM
120/208/1 phase wiring questions JohnJon Electrical 11 08-31-2008 11:28 PM