2x100a sub on service main
Is it possible to feed 2x 100A subpanels on a 200A service main?
The subs are one 6space mainlug...6=20A circuits, and the second 24space mainlug... 15=20A circuits and two 30A circuits not connected as of yet. The 200A service main panel has 14=20A and 2=30A existing circuits that are powered. Or do I need a new service main for the second subpanel? Thanks |
10 ft. Rule: The conductors must terminate into a 100 A circuit breaker They must be enclosed in conduit. You CANNOT use a cable for this The conductors must be rated for the load you serve, and in no case shall they be smaller than 1/10 the capacity of the main. So, if you install the panels within 10 ft. of the main, you can tap that with an approved method, and feed the two 100 A panels. Each 100 A panel must have a 100 A main of it's own, and you can use #3 copper with a #8 ground. 25 ft. Rule: All of the above rules, except the capacity of the tap conductors shall not be less than 1/3 the size of the main. So, if you can do the exact same thing as I suggested above except you cannot exceed 25 ft. InPhase277 |
YOu can have as many panels as you want. As long as the load is under the calculated service load.
He did say "on a 200 A service main"... InPhase277 |
Thanks guys! yeah I wanted to feed out of the 200A service main, so Ive got #3 thhn stranded copper going to run to the farthest sub 24-space(40ft. from the 200 service main) fed with a 100A breaker. And #4 thhn stranded copper gonna run to the 6-space sub ( 4ft. right behind the 200 service main) fed with a 100A breaker(or should I use a smaller breaker?). All one building no detached rooms.
InPhase277 |
Install 4 wire feeders. No main bonding jumper at the sub panels (keep ground and neutral separate). Stay below a 85 amp breaker on the #4, an 80 amp would be good.
Thanks yeah I will run 4wire feeders in 2" pvc and use an 80A breaker for the #4 wire. Could you enlighten me on how to calculate the amps used in the panels to make sure it doesnt go over the main breaker Amp?
I agree but I would just like to know and hear your explanations on load calculations.
This is something you cannot just explain in a text, this is why our job is what it is, years of experience and training... some things are just not DIY... |
Thanks...One more question..on that 100Amp subpanel, I ran three wires of #3 thhn for the two Hots and Neutral from the Main 200A to the Subpanel.
Can I run the ground separate (not to the main panel) outside to a ground rod which is a shorter run with the remaining # 3 wire that I was short? If so, do I still separate the neutral and ground at the Sub? |
| All times are GMT -4. The time now is 09:46 PM. |