#1 |
24VAC when light switch is off???
I'm changing a light fixture in my kitchen, and while testing voltages to make sure power was off, I found I was getting 24 volts AC in the box while my switch was turned off. Switch on is 120.
Is it possible my switch is failing and letting some voltage through? |
#2 |
Electrical Contractor
Are you testing with a meter?
Chances are it is phantom voltage. Turn the breaker off.
Yes I am a Pirate, 200 years too late. "Jimmy Buffett" |
#3 |
Yes multi-meter. I'm not worried about getting electrocuted I'm worried about faulty wiring or failing components. Don't want to damage the new fixture either.
#4 | |
24VAC when light switch is off???Quote:
More commonly known as "PHANTOM VOLTAGE" Its not unusual for digital meters with high input impedance to pick up these voltages. If you want to be sure, put a load, such as a light bulb on the wire. If the voltage goes away, then for sure its a phantom voltage. |
#5 |
Lighted switch?... Dimmer?
#6 |
It was phantom voltage... thanks for the tips. I also tested the resistance through the switch to be sure it wasn't failing and it didn't register with switch off so switch is ok.
| Display Modes | |
| Wiring in a 4-way Switch | RickSene | Electrical | 5 | 04-09-2013 08:25 PM |
| Hot wires on both sides of switch | RedRumLoki | Electrical | 4 | 11-20-2012 10:37 PM |
| Replace bathroom light switch with dimmer switch | ToddD | Electrical | 11 | 05-06-2012 06:58 PM |
| Motion Light tripping GFCI? | Jonobp | Electrical | 5 | 09-07-2009 08:52 PM |
| Confused by switch w/indicator light install... | WaldenL | Electrical | 7 | 08-29-2009 10:02 AM |