Old 11-01-2009, 02:44 AM   #1
240v to subpanel with 4x 120v circuits
hello. I am new on this forum and I am just wanting to be sure if I am doing the right thing here.
240v goes to subpanel that has 4x20a 120v breakers. each breakers is hooked to an outlet - in this case it has 6 outlets:
circuit1= one outlet
circuit2 = two oulets
circuit 3 = two outlets
circuit 4 = one outlets
here are the photos and please let me know if the hookups are correct.
240v to subpanel with 4x 120v circuits-240voutsidepanel.jpg   240v to subpanel with 4x 120v circuits-insidepanel_label2.jpg   240v to subpanel with 4x 120v circuits-insidepanel_label.jpg
synstealth is offline   Reply With Quote
Old 11-01-2009, 05:50 AM   #2
How many wires are in that cord? What gauge is the cord? What is the ground wire connected to? From the looks of the plug, it's a 6-30P, which is used on straight 240V appliances. What is this setup going to be used for?
jerryh3 is offline   Reply With Quote
Old 11-01-2009, 07:13 AM   #3
Licensed Pro
You CANNOT use the green wire as a neutral. You MUST use a 4-wire cord and receptacle that has two hots (black-red), a neutral (white), and a ground (green-bare). The feed to the receptacle must also be 4-wire.
Old 11-01-2009, 07:25 AM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,948
HH is completely correct.
You MUST have a 120/240v circuit, or a straight 120v circuit to power that panel. DO NOT use it on a straight 240v circuit as it is wired now!
As it stands, that whole thing is dangerous and SHOULD NOT be used!!!!!
Old 11-01-2009, 07:33 AM   #5
But, it's for the band, man. Big gig tonight.
Old 11-01-2009, 07:40 AM   #6
Well that makes all the difference. That and sanding the floor, right?
Old 11-01-2009, 07:45 AM   #7
Hell no. I tie right into the main lugs with alligator clips for a floor sander.
Old 11-01-2009, 09:27 AM   #8
so you are saying I need to put in a 4 wire 240v cord to the breaker and use 120/240v receptacles to make this work?
3 wire in that cord. ground is connected to the breaker box metal surface (body unit)
setup used to plug in an 240v outlet that can power up 120v applicances such as power tools, industrial lamps and a microwave all producing at least 5000 to 6000 watts at once
which is why i came up with 240v and split in 4 120v circuits
please help me out on a better solution to get this done right.
Old 11-01-2009, 10:28 AM   #9
anyone?
Old 11-01-2009, 10:32 AM   #10
Ok. Let's start from scratch. You can't make 120V outlets from a 240V outlet. You can, however, make them from a 240/120 outlet. For this you'll need a four wire cord with a four wire plug/receptacle. L1/L2/N/G. L1 and L2 to the bus two bus bars which you have correct. The neutral wire will connect to an isolated bar in the sub panel. The ground will connect to a bar which is bonded to the sub panel. The way you have it set up right now, the receptacles are not grounded and the ground wire at the receptacle is acting as the neutral. No bueno.
Old 11-01-2009, 10:46 AM   #11
what happens if the 240v(3wire) input to panel COMES from an 240v OUTLET (receptacle) which is why I made the plug so i can just plug it in...
the panel is supposed to be portable, I want a 240v plug where I can just plug it in and use... what can I do about this issue?
suggestions?
Old 11-01-2009, 10:57 AM   #12
Rewards Points: 2,350
suggestions?
Do what the others have suggested and use a 4-wire cord. A dryer or range cord should be readily available in 4-wire.
The way it is now may work, but it is not correct and could be quite dangerous depending on how the receptacle that you plug into is wired. Also, judging by the white cable going to the receptacles on the board, I'm guessing that is 14-2, so you need to use 15 A breakers, not 20 A.
Old 11-01-2009, 11:09 AM   #13
the 240v plug is 3 prong looks like this: (-.-) is there a 4 wire for this plug?
4000watts on a 120v circuit (knowing that one receptacle can support only one 1000w app) so I built 4 circuits to run them all at once.
Old 11-01-2009, 11:15 AM   #14
can I add a ground wire along with the 3 wire 240v? as an single shielded ground wire so it can act as 4th wire (same gauge of course) instead of replacing 3 wire with an 4 wire?
No, there is not. That is a straight 240 plug. You could just use a dryer cord/receptacle if 30A is sufficient.
Old 11-01-2009, 11:15 AM   #15
NO.
That is a 3-wire straight 240v plug. You need a 4-wire cord AND plug AND circuit. You need a neutral along with the two hots and ground.
240v Air Compressor to 120v help ruacoltsnut General DIY Discussions 10 11-11-2010 04:05 PM
Do you think a tool running at 240v works better than at 120v? Piedmont Electrical 39 07-03-2009 09:50 PM
2008 NEC - 120V and 240V receptacles on the same MWBC? ScottR Electrical 10 06-05-2009 10:39 PM
120v for shed from 240v HotTub circuit? MrMark Electrical 6 04-06-2009 12:43 AM
Understanding 120V branch loads in 100A 240V system WaldenL Electrical 17 02-17-2009 09:15 AM