stickboy1375, i appreciate all the help and time, thanks!
1percenter is offline   Reply With Quote
Old 06-19-2012, 01:08 PM   #17
Rewards Points: 794
Are you sure you need 50A? That sounds like a very large feed for a compressor. 50A @ 240 V is 12,000 watts or 16HP! Say 10HP after allowing for start up surge. 10HP is a pretty big motor. I don't even know if you can get single phase motors that big, you're creeping into 3Φ territory. How big is the motor on this thing?
curiousB is offline   Reply With Quote
Old 06-19-2012, 02:23 PM   #18
oh not at all, its just what i found searching online, i would be okay with a 30amp and even possibly a 20amp.
My compressor is a 5hp which draws about 16amps under 80% load and 22amps at start-up.
Old 06-19-2012, 05:32 PM   #19
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
You still have to use Table 430.248 to size a motor, a 5 HP motor ends up being 28 amps at 240 volts...
We have to add 125% to that value for minimum branch circuit wiring, 28 x 1.25 = 35 amps, 310.16 allows #10 AWG @35 amps...
Main Electric Panel Help Redrum Ninja Electrical 13 10-22-2011 07:28 PM
200A upgrade and move, backfeeding permitted? WillK Electrical 3 05-30-2011 08:00 PM
Two sub panels off of main panel OK? brjl Electrical 4 05-29-2011 01:33 PM
Replace main panel? And lots of other ?s Bcoleman6 Electrical 13 01-22-2008 09:40 AM