Old 12-12-2008, 12:55 PM   #1
Question
240V Electric Heater install - 3 wire vs. 4 wire?
I'm installing a 240V 40A electric garage heater. I expected to wire 2 hot (blk/red), neutral (wht) and ground (grn) but the heater only has 3 lugs. The ground lug's wire hole is much smaller than the hot lugs. Is this a pure 240V install where both neutral and ground are not needed? If so is the neutral/ground wire a smaller gage than the hot wires? I was going with 6-8 Gage, OK?
dhgarage is offline   Reply With Quote
Old 12-12-2008, 01:22 PM   #2
Does the heater draw 40 amps, or does it require 40A protection? Can you post the model number. You are most likely correct. It is a three wire connection(hot, hot, ground). The ground will be a reduced size(most likely 10AWG)
jerryh3 is offline   Reply With Quote
Old 12-12-2008, 02:15 PM   #3
Ouellet Model# OASU10000T Specs show: Volts=240; Amps=41.67; Watts=10,000; BTU=34,120. For wire I'm thinking of using 8/8/10 gage (hot/hot/ground) unless 6/6/10 is recommended.
Old 12-12-2008, 02:40 PM   #4
Electrical Contractor
6/6/10
hpp58 is offline   Reply With Quote
Old 12-12-2008, 03:07 PM   #5
joed's Avatar
The unit draws 41 amps. You need a 60 amp breaker. #6 wire required.
Old 12-12-2008, 11:14 PM   #6
I just purcahsed same heater and came on here looking for help. i plan on pulling wire from my main panel to my attached garage. it will take about 90 feet of cable for this. For that reason i think i will do a 100 amp lug panel in garage with a couple extra future circuit capacities. i have not pulled cover off my heater but is this correct that it will only have 2 hots and a ground?? No neutral?
I am thinking 2/2/2/4 aluminum for run to lug box then 6 awg for panel to heater 60 amp breaker.
i will have electricain make final connection but because of complexity of cable pull trying to save some $$.
Most of the equipment i have serviced installed in past ( vacuum sytems and air compressors for denatl offices) used 2 hots neutral and ground. lack of neutral seems odd but i can understand why maybe its not used.
Can someone clarify for me? Also does the 2/2/2/4 aluminum sound like good choice?
Ryan
ssscamaro is offline   Reply With Quote
Old 12-12-2008, 11:24 PM   #7
[quote=ssscamaro;197351lack of neutral seems odd but i can understand why maybe its not used.
Ryan[/quote]
I believe the the leg that is out of phase is used as the neutral.
I had an addition done a couple years ago and they used the 2/2/2/4 alum. to feed a sub panel with a 100 amp breaker in the main.
Plumbvoltage is offline   Reply With Quote
Old 12-12-2008, 11:49 PM   #8
Res Ipsa Loquitur
Originally Posted by ssscamaro View Post
lack of neutral seems odd but i can understand why maybe its not used. Can someone clarify for me?
Neutral is only needed in this situation if there were a need for 120v in an appliance such as with an electric range which has both 120v and 240v loads. For a straight 240v item, no neutral is necessary and would not likely have a connection point. You do need the ground though.
Did you ever stop to think, then forget to start again?
handyman78 is offline   Reply With Quote
Tags
240v, 40 amp, garage heater, wiring
new electric water heater - Vacuum breaker necessary? J187 Plumbing 12 05-26-2012 09:42 AM
Adding a wall switch to a pull chain fixture abacuslearns Electrical 17 12-20-2011 07:02 PM
Install of Replacement HW Heater DIY In King George Plumbing 19 01-12-2007 08:49 AM
Baseboard heater Help! jweinstock Electrical 6 10-28-2006 05:01 PM
Periodic release from (I think) the T&P valve on the water heater alexz Plumbing 3 08-15-2006 11:31 AM