240 To 120 Circuit Conversion - Electrical - DIY Chatroom Home Improvement Forum
Old 02-09-2009, 11:34 AM   #1
240 to 120 circuit conversion
I have removed my old 240V electric range and have switched to gas. I now have three #8 conductor wires in a metal conduit on a 40A breaker that I would like to convert to 120V. There is no ground wire in the conduit (1960's wiring). Can I run a separate ground from the main supply through the conduit and then set a sub-panel on this circuit or would it be better to pull through a whole new set of conductors? Thanks
mark57 is offline   Reply With Quote
Old 02-09-2009, 11:46 AM   #2
*****IF this is metal conduit all the way to the panel*****, the conduit serves as a ground.
Cap off one hot conductor and wirenut a short pigtail onto the other hot and the neutral (white).
Install a short #12 bare ground wire from the box to the 120v recep via a ground screw (there will be a tapped 10/32 hole in the back of the box)
Remove the 2 pole 40 amp breaker and install a single pole 20. Cap off the leg you are not using and install the other on the breaker. If your breaker has a screw terminal rather than a lug, you will probably need to wirenut a short @12 pigtail there too.
Put a panel blank or a spare breaker in the remaining slot. Spare breaker is better. It won't fall out every time you take off the dead front.
220/221 is offline   Reply With Quote
Old 02-09-2009, 12:34 PM   #3
Rewards Points: 508
Send a message via AIM to theatretch85
The OP should be able to check for continuity between the conduit ground and the existing neutral wire to verify this since they should in theory be tied together at the main panel.
I would agree with 220/221's plan to re-wire using the existing wires and dropping them to 12 gauge to make the connections to the outlet and breaker. Most 20 amp breakers will not accept wire larger than 10gauge wire, you will just have to look at what your new breaker is rated for.
theatretch85 is offline   Reply With Quote
Old 02-09-2009, 12:38 PM   #4
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
The OP wants to run a subpanel off this circuit. I would pull a ground in since it's pipe the whole way. I'm not fond of using pipe as a ground (my opinion) especially something 30-40 years old.
I'm just wondering why you wouldn't want a 240 volt sub?
wirenut1110 is offline   Reply With Quote
Old 02-09-2009, 12:40 PM   #5
AH - sub-panel, I'd do a 240v sub
Old 02-09-2009, 12:59 PM   #6
Thanks for the advice. I didn't say it but when I said sub panel I meant 240V. I think a sub panel would give me the most options. I am not sure how I feel about using the conduit as a ground either, but that would certainly be the easiest thing to do. I never thought about the 20A breaker not accepting larger wire, that is certainly something to check before I jump into it. Thanks again
Old 02-09-2009, 02:36 PM   #7
A sub panel simply to supply a 120v recep behind the gas range?
A sub panel behind the range?
You're killing me here
Old 02-09-2009, 02:38 PM   #8
And where did he say all that???
Need a wiring diagram Mooreski Electrical 47 02-01-2015 03:07 PM
Wiring a single pole switch into a 220v circuit rlmorgan Electrical 38 10-15-2008 07:59 PM
Problem with circuit breaker. HELP! spartanic Electrical 2 10-28-2007 03:09 PM
So lost - electrical requirements please help lapsis9 HVAC 4 12-20-2006 08:09 PM
Adding new circuit breakers to 100 amp sub panel DrP Electrical 8 05-25-2006 10:05 PM