So, I decided to perform a service upgrade since I just finished installing an underground service lateral.
I believe the service upgrade falls under the NJ rehab code, so NEC 2005 would apply.
To the point, I would like to use 4/0 SEU to supply a 225A load center within about 18 inches of the meter pan. Can I use the 90 column under NEC 2005, which yields 205A, allowing me to use the next size up?
If not, I don't even know where to buy 3/0 copper SEU by the foot. Of course, I can get 3/0 THHN ($6/ft. per conductor) and 250 kcmil Aluminum, but 2" rigid conduit would be extremely difficult to install in the present location.
I could put in a 200A main breaker, but I foresee the day when I will need the extra 25A, as I add more 7 kilowatt mini splits, etc. 320A service is not an option, since the service lateral is 4/0 aluminum triplex.
CL200 meters with 225A service:
http://www.inspectorsjournal.com/forum/topic.asp?TOPIC_ID=1438
itsnotrequired 04-14-2012 11:25 AM
you'll have to use the 75 degree c ampacity columns. i highly doubt your panel is rated for 90 degree c terminations.
k_buz 04-14-2012 11:27 AM
I have never seen CU SER. Also, I would check somewhere else on that 3/0, I just priced 1/0 at $1.13/foot.
itsnotrequired 04-14-2012 11:31 AM
they make it but i don't believe it is used very often. aluminum is just so much more cost effective.
http://www.southwire.com/products/SEUSERSEOEM.htm
a_lost_shadow 04-14-2012 12:37 PM
I'll second that check other places for prices. Even the big box stores can beat $6 a foot. I believe my local Lowes is ~$4 a foot. The electrical supply house I used (platt.com) appears to also offer those sizes cut to length. They want $1.37/ft for 250 XHHW-2 Au and $3.35/ft for 3/0 THWN-2 Cu.
Actually, as I look some more are you sure you didn't get a price on XHHW Cu? Platt apparently wants $5.57/ft for it.
benjamincall 04-14-2012 12:43 PM
So, I've got to use invidual conductors in some sort of conduit?
Here's my panel:
http://products.schneider-electric.u...ber=QO142L225G
I haven't bought a main breaker yet, but this is the one I want to use:
http://products.schneider-electric.u...countrycode=us
benjamincall 04-14-2012 12:55 PM
Must have been XHHW. If I can figure out some way to accommodate the conduit, do you think the 225A service will work? Just to recap:
135' (from the top of the pole) 4/0 aluminum triplex through 3" conduit, CL200 meter, 4/0 Cu or 250 Al in 2" PVC to the 225A load center.
Edit: The 75 column gives me 200A for 3/0 copper, so I guess I would have to go the next size up.
Speedy Petey 04-14-2012 12:59 PM
Is this a residential service?
benjamincall 04-14-2012 01:04 PM
Yes, this is for my home.
a_lost_shadow 04-14-2012 01:05 PM
You don't have to use single conductors. However, it's going to be easier to pull. Depending on what you're local supply houses stock, or what you find online. It may be cheaper and easier to find going single conductors.
Looking at the cut sheet from one manufacturer, it appears that they don't make 2 conductor w/ground SER cable larger than 4/0 Au. So you'd need to go up to 3 conductor w/ground for your service entrance. Doing the conduit fill calculation, I see that you'll also need 2 1/2" RMC to meet conduit fill.
Also remember if you go with a cable such as SER or SEU, you need to do the conduit fill based upon the outer diameter, or largest outer dimension for non round cables like SEU.
a_lost_shadow 04-14-2012 01:09 PM
For residential main service you can often use NEC Table 310.15(B)(7) (I think it was B6 before 2011). This calls for 3/0 Cu or 250 mil Au for 225.
Speedy Petey 04-14-2012 02:21 PM
Just use 4/0AL or 2/0CU like any other typical 200A service.
Is this really a 225A load center, or a 200A main breaker panel?
If it is really 225A, where did you get it and where is the main breaker?
benjamincall 04-14-2012 03:01 PM
Here's my panel:
I haven't bought the main breaker yet, but this is the one I want to use:
Petey,
I bought the panel from a supply house on eBay. It's an MLO panel to which I'm going to add a 225A main breaker (above).
Speedy Petey 04-14-2012 03:58 PM
Originally Posted by benjamincall (Post 898891)
Petey,
WHY in the world did you buy that? Why not just get a standard main breaker panel?
electures 04-14-2012 06:16 PM
New Jersey has updated the ReHab Subcode to reference the 2008 NEC. Good thing I just updated this post a week ago to reflect the change.
http://www.diychatroom.com/f18/diy-e...jersey-106961/
If you have any questions let me know.