Old 05-25-2012, 03:44 PM   #16
It was a dark and stormy
Yoyizit's Avatar
220v in garage help.
Originally Posted by Missouri Bound View Post
Oddly enough, you can maintain the 12 ga. with a 30 amp breaker in this instance. The NEC has allowances / specifications for this type of situation....and this type only.
While we're on the subject,
if this is true,
why does the NEC force us to buy #12 AWG worth of copper for "only" 20A?
You have a code cite for this 30A case?
TIA.
Old 05-25-2012, 04:35 PM   #17
Licensed electrician
Conductor sizing for motors is different than for general purpose branch circuits.
The breaker is sized to allow the startup current while the conductor is sized for the run current.
Old 05-26-2012, 08:17 AM   #18
Yoyizit's Avatar
Does anyone agree with this?
A 30A breaker on #12 does not seem to adequately protect the wire if other applications call for a 20A breaker.
Old 05-26-2012, 09:51 AM   #19
A "Handy Husband"
rjniles's Avatar
Yes I agree with Jim Port.
here is a good reference from another poster (Electures)
Sizing Motor Branch Circuit Conductors and OCPD's
Coastal South Carolina
Old 05-26-2012, 11:50 AM   #20
E2 Electrician
stickboy1375's Avatar
Because, the breaker is only providing ground fault and short circuit protection, the motor contains the overload protection... and you can only do this when the motor is hard wired, not cord and plug connected.
stickboy1375 is online now   Reply With Quote
Old 05-26-2012, 11:54 AM   #21
Licensed Electrician
k_buz's Avatar
I see no indication of internal overload protection.
k_buz is online now   Reply With Quote
Old 05-26-2012, 12:07 PM   #22
E2 Electrician
Only a picture of the actual nameplate on the motor would tell us that...
But Im betting it's already in place. With that said, most compressors that are bought are inflated with an unrealistic HP rating.... as a sales gimmick.
Old 05-26-2012, 12:32 PM   #23
k_buz's Avatar
I wholeheartedly agree that if there is internal overload protection (protection at 25A or less) it would be compliant to run 12's on a 30A breaker. BUT, I would not tell someone to put 12's on a 30 without proof there actually is protection built into the motor.
Old 05-26-2012, 02:08 PM   #24
Yoyizit's Avatar
Thanks for the link.
I'll have to chew on this rule for a while.
I was under the impression that to give long life to wire insulation and to prevent igniting nearby combustible materials, breakers provided protection for all levels of overload, bolted shorts and otherwise. Is this incorrect?
Maybe mild overloads (2x rated current, 3x rated current) are so infrequent compared to dead shorts that the NEC doesn't worry about this?
Old 05-26-2012, 03:10 PM   #25
E2 Electrician
In certain applications, yes, you are incorrect.
For motors, Breakers only supply ground fault and short circuit protection.... generally, anything over 10 HP will have external overload protection, but anything smaller will generally have overload protection built into the motor.... So, as long we follow article 430 in the NEC, everything is okay.
Another great pic....
The Following User Says Thank You to stickboy1375 For This Useful Post:
Yoyizit (05-26-2012)
Old 06-05-2012, 04:45 PM   #26
haven't done anything yet.... but i figure i would ask.
Can i "borrow" some 220 from the AC? would that be easier? it is right next to my garage and we never use the AC (compressor will also be used a handful of times) would that work?
or would a "rv temporary outdoor" box at the panel work as well?
1percenter is offline   Reply With Quote
MWBC to Garage Questions benleef Electrical 3 02-22-2012 12:02 PM
220V 15A outlet in Garage curiousB Electrical 97 01-27-2012 10:53 PM
220v service for garage chevelle Electrical 2 11-11-2011 06:23 AM
How to wire a detached Garage? (w/ Conduit?) FLintonRice Electrical 7 06-27-2011 02:08 PM
Pouring Concrete Slab in a small rickety garage. RORO Building & Construction 0 10-19-2010 04:56 PM