Old 07-19-2012, 09:50 PM   #1
220v electric range
I live in an area that has recently been plagued with power outages although I am lucky enough to say that I have only lost half my power. Thus giving me only one 110v power source down one side of my box. Is there a way that I can rewire my range connection to operate off one side of my box until service is restored?
js77 is offline   Reply With Quote
Old 07-19-2012, 10:48 PM   #2
220v electric range
No....i'm pretty sure you can't....how long does your power look to be out for?
ryan50hrl is offline   Reply With Quote
Old 07-19-2012, 11:00 PM   #3
220v electric range
They are telling me several days. I have already reconfigured my box to supply as much power throughout the house as possible, but am trying to figure ways to cook and get hot water. Since that's electric also.
Old 07-19-2012, 11:09 PM   #4
Master Electrician
220v electric range
Not going to happen. And you've probably seriouly unbalanced your panel by shifting stuff around. When powers restored move it all back.
How do you only lose one leg in an outage?
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
Old 07-19-2012, 11:58 PM   #5
Licensed Electrician
k_buz's Avatar
220v electric range
You know, moving the breakers around MAY have created a fire hazard. If you have both legs of a multi wire branch circuit on the same phase, the neutral could become overloaded thus creating a fire hazard.
Not a fan of the new layout.
Old 07-20-2012, 12:25 AM   #6
220v electric range
No Bro...!
Don't do that... You can easily double-phase neutral on three wire circuits, causing open circuit neutrals and equipment/appliance damage, let alone a code and safety violation that could cause a fire.
kontoose is offline   Reply With Quote
Old 07-20-2012, 06:47 AM   #7
Licensed Electrical Cont.
Speedy Petey's Avatar
220v electric range
Can you explain how moving a breaker can cause an open neutral ?
The Following 2 Users Say Thank You to Speedy Petey For This Useful Post:
mpoulton (07-20-2012), stickboy1375 (07-20-2012)
Old 07-20-2012, 11:23 AM   #8
220v electric range
Thanks for althe feedback with my problem, but the electric company has informed me that there is damage to the transformer which has cause my bazaar half outage. So I have decided to leave it alone and wait.
Old 07-20-2012, 03:51 PM   #9
It was a dark and stormy
Yoyizit's Avatar
220v electric range
Running a 220 appliance on 110 will give you 1/4th of the power and maybe >4x the cooking time.
Old 07-20-2012, 06:56 PM   #10
220v electric range
In short ! It cannot be easily and safely done !
It is technically possible,
but many problems would come with it !
safety and code wise.
Best not to do it !
Easier to just get an 220v genny !
dmxtothemax is offline   Reply With Quote
Old 07-21-2012, 01:36 AM   #11
220v electric range
The electrical arc, (or initially - spark), under a loose or bad connection is -- although minute at first -- is around 3,000 degrees C. Each time the arc strikes, it erodes and bites into the copper (or aluminum) at the node. This deposits either copper oxide, or alluminum oxide at the node, and the heating further loosens the alkready bad connection.
Here is born the vicious cycle.
The more the arcing the more the deposit the less the copper surface area...the resistance goes up at the node, and the cycle intensifies...until the connection is broken...and yes - a by product of this cycle is burnt insulation - which may cause a short...but matter not, the end result is...an open.
(Homework is advise for you my boy...but, in the form of...[many years] of experience.
Whooo ah, ahh, hahahaha (Daemonic laugh).
(Thank you for your participation).
Old 07-21-2012, 02:09 AM   #12
Master Electrician
220v electric range
if being at trade for 40 years leaves me like that i'm going back to school monday and i'm going to be an accountant.
The Following User Says Thank You to andrew79 For This Useful Post:
Speedy Petey (07-21-2012)
Old 07-21-2012, 07:32 AM   #13
k_buz's Avatar
220v electric range
I brought that part up because of the above quote.
Old 07-21-2012, 09:01 AM   #14
220v electric range
I would suggest putting all the breakers and the wires they feed back in their original positions for starters for now.
Then work on finding out which breakers feed multiwire branch circuits (usually one on each MWBC has a red wire attached) and plan on what needs rearranging.
... how moving a breaker can cause an open neutral ...
Overloading the neutral of a MWBC can result in loose connections from overheating developing en route over time (circuits daisy chain from one receptacle to the next). Should the neutral path go bad then you get all the wolfy problems described above.
Some older electric stoves will provide low to medium heat on some of the knob positions on some of the burners when one of the hot feed wires for 240 volts is out.
You may make a 240 (220) volt electric water heater work on 120 volts by unhooking the white wire of its feed from the respective breaker and connecting that white wire to the neutral bus. (Move the black wire to the other half of the breaker if it was originally on the dead half) Expect the recovery time (heating of the next tankful of water) to be more than twice the normal time).
I am guessing that a 120/240 volt electric stove can work on 120 volts by doing this: Find its 3 wire cable and breaker. Turn off the breaker. Unhook that cable white wire from the neutral bus and tape over the end and label it. Unhook the (red or black) wire from the dead half of the breaker and connect that wire to the neutral bus. Caution: I cannot rule out undesirable side effects to the clock and timer and other 120 volt components in the stove which are now getting roughly 60 volts, the exact amount depends on how the burners are switched into the circuit at that moment.
The average homeowner who lost his house in the Oklahoma tornadoes should move for good and not rebuild. Too much complexity watchdogging the contractor. Too much a chance to be defrauded.
Old 07-21-2012, 01:25 PM   #15
Master Electrician
220v electric range
Originally Posted by Silk View Post
If you put both breakers on the same side of the phase (because the home only has 1 phase with the neutral bonded to the middle of that phase, so stop talking about "phases") an open neutral will cause an open circuit with zero current flow, thus resulting in zero voltage drop across the appliance, thus the appliance is safe.
Your open neutral scenario burning out the loads only applies on a true MWBC.
So, if you have seen this literally hundreds if not thousands of times..... You have been mistaken literally hundreds if not thousands of times....
Shine on
Somehow i just don't think my wording would have been this good if i had said this. Nicely put
Roper Electric Oven Range Problem mcnutty Appliances 6 07-05-2011 06:32 PM
Wiring Electric Range Ringo2 Electrical 6 05-23-2011 06:49 PM
Electric to gas range Manis Appliances 9 02-01-2011 03:24 PM
Wiring for electric range rgustavw Electrical 2 09-21-2010 03:18 AM
Need help on Electric range wiring rarquilla Electrical 20 11-20-2008 08:00 PM