220V & 110V Outlets - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 05-11-2011, 03:08 PM   #16
Semi-Pro Electro-Geek
Rewards Points: 2,938
Originally Posted by rjniles View Post
I would like to see the reference where you found this.
The NEC is generally restrictive, not permissive. If something is not prohibited by the code, it is allowed. Note that HouseHelper did find a provision that specifically addresses this, though.
mpoulton is online now   Reply With Quote
Old 05-12-2011, 01:20 PM   #17
Licensed Pro
I have reread that exception and exception #1 about 3 or 4 times and do not believe the intent is to allow the use of multiple line to neutral and line to line loads on the same MWBC. Maybe we need input from one or more of the working electricians on this forum.
I am a "working electrician" and this is definitely allowed... this is no different than a dryer or range circuit, which is a 120/240V MWBC!
Old 05-12-2011, 03:26 PM   #18
licensed electrician
here it is straight from the nec
210.4(C)
Line-to-Neutral Loads. Multiwire branch circuits
shall supply only line-to-neutral loads.
Exception No. 1: A multiwire branch circuit that supplies
only one utilization equipment.
Exception No. 2: Where all ungrounded conductors of the
multiwire branch circuit are opened simultaneously by the
branch-circuit overcurrent device.
The Deez is offline   Reply With Quote
Old 05-12-2011, 04:21 PM   #19
IBEW Electrician
210.4(C)
This section to me has been a topic of confusion more than once, but im leaning in the direction that you MAY do this as long as they are the same amperage, and have a simultaneous disconnecting device, thinking logically, if EITHER of the two legs exceed amperage, it will trip both legs, and on the other end if you need to shut of either of the circuits for service, you will be forced to shut off both to eliminate the hazards of neutrals....
Scott3229 is offline   Reply With Quote
Old 05-12-2011, 04:55 PM   #20
Agreed, I've only been a licensed electrician for about 10 years. All i have to go by is past experience, and i can honestly say that I haven't done this, nor would i do it and I can think of LOTS of times I had the opportunity to do this wiring method. If it was me and in my opinion i would just run a 12/2 for the 120v stuff and leave the 240v stuff on a dedicated circuit. This is an interesting topic though, I have a meeting with a state inspector tomorrow in Boston for a job, I'm gonna run this by him and see what his opinion is. Maybe he can reveal a secret code article.
Old 05-12-2011, 05:54 PM   #21
Electrical Contractor
kbsparky's Avatar
I'd opt for a sub-panel to replace the dryer outlet. Then one could run 120 Volt circuits for the standard receptacles, and a separate 240 Volt circuit for the radial arm saw. Separate breakers for each circuit.
-KB
Old 05-13-2011, 01:16 PM   #22
210.4(C)
I don't see any ambiguity whatsoever. A MWBC with a double-pole breaker is clearly permitted to supply both 240 and 120V loads. That's the entire point of Exception 2.
220v vs 110v Baseboard Heater?? Master Brian Electrical 8 11-19-2010 11:13 PM
220v to 110v extension cord? glamabilly Electrical 14 09-25-2010 11:25 PM
Main box feeding 220v and 110v brearker box off a 50am breaker? uvamosk Electrical 30 10-14-2009 10:46 PM
Adding 110V outlets to 220V line MarcG Electrical 25 04-29-2009 06:04 AM
Convert 220V to 110V wrldruler Electrical 13 09-15-2008 11:55 AM