Hello, everyone.
I'm wiring up some receptacles in my new garage workshop, and have some questions.
I have one tool - a radial arm saw - that is 220V / 7A. All my other power tools are 110V. As a hobbyist, obviously I'd only ever be running one tool at a time, although my dust collector - 110V / 5A - would be running whenever any of my 'dusty' tools was.
In the garage at the moment is one 220V outlet, four prong, for a dryer. It is connected to a 30A double pole breaker. We are buying a gas dryer, so will not be using it for a dryer.
My plan, subject to the opinion of the experts here, is to replace the 220V outlet with a box, and run hard conduit from that around the wall to where I want my outlets. I'm going to drop three or four receptacle boxes from that, each with 2 x 110V & 1 x 220V outlet in it. That will give me flexibility to move tools later as I see what layout works.
Here's the electrical question....
1) Is it acceptable to provide the 110V to the outlets by using one of the two hot legs of the 220V, or do I need to pull a three conductor wire for the 110V in addition to the wire for the 220V outlet?
2) Since the RAS has only a three-pin plug, Hot-A, Hot-B and Ground, is there any reason to even pull 4-conductor wire for the 220V if I pull separate wire for the 110V? Obviously if I can use one of the hot legs of the 220V for my 110V then I have to pull four conductor because I need the common neutral, but if I can'y can I just use three conductor wire for both?
Thanks for your help,
Richard
rickinnocal is offline   Reply With Quote
Old 05-11-2011, 12:57 AM   #2
Scared Electrician
Saturday Cowboy's Avatar
u must have/use 4 wire.
Ragged Trousered Philanthropist
Please follow the code - its there for your safety no matter how inconvenient.
Saturday Cowboy is offline   Reply With Quote
Old 05-11-2011, 12:59 AM   #3
Semi-Pro Electro-Geek
Rewards Points: 2,892
You can do this, but you'll need to replace the 30A breaker with a 20A. You can run four wires: two hots, neutral, and ground. The 120V loads go from either hot to neutral, and the 240V receptacles (make sure to use a 240V receptacle type!) go between the two hots. I installed a few circuits like this in my old shop (not re-using an old circuit, though). The way I arranged it, I installed double gang boxes. Each box had one duplex receptacle, and one 240V 20A receptacle. The duplex was split so the top half was on one hot and the bottom was on the other. That way I could run two high-current 120V tools from the same outlet.
mpoulton is offline   Reply With Quote
Old 05-11-2011, 01:17 AM   #4
Originally Posted by mpoulton View Post
...The 120V loads go from either hot to ground...
Don't you mean from either hot to neutral?
...The duplex was split so the top half was on one hot and the bottom was on the other. That way I could run two high-current 120V tools from the same outlet.
Yes, that was what I was planning.
Richard
Old 05-11-2011, 04:05 AM   #5
Yeah, I can't believe I wrote that. Edited.
Old 05-11-2011, 07:39 AM   #6
Rewards Points: 1,440
YOu can run 3 conductors (hot, hot, ground) to an outlet box with nothing but a 240 volt only receptacle in it.
If you run the feed to a new subpanel, you can keep the 30 amp breaker at the main panel. The subpanel would have double wide double breakers for any 240 volt circuits and any circuits where two hots (on opposite sides of the line) share a neutral.
Old 05-11-2011, 08:49 AM   #7
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,142
Is this garage a detached structure from the house? Or is it attached? The answer to that question makes all the difference in the world.
Assuming it is attached: You can not use a single circuit to provide both 120 & 240 volt receptacles without a sub panel. You cannot use the existing 3 wire dryer circuit to add a sub panel as it requires 4 wires. What you could do is use the existing dryer circuit to provide a 240 volt circuit for your saw. Change the breaker to a 15 or 20 amp double pole. Run a new 12-2 cable from the breaker panel to install the 120 volt receptacles.
If the garage is detached, ignore what I have said above.
Coastal South Carolina
Old 05-11-2011, 09:19 AM   #8
Originally Posted by rjniles View Post
You cannot use the existing 3 wire dryer circuit to add a sub panel as it requires 4 wires. What you could do is use the existing dryer circuit to provide a 240 volt circuit for your saw. Change the breaker to a 15 or 20 amp double pole. .
Hmmm. Didn't he say that the original existing dryer receptacle was 4 prong ergo fed with 4 conductor cable?
The saw, meanwhile, was 240 volt only with 3 prong plug (one ground prong).
Hmmm. You mean you can't run a traditional MWBC* (a 120/240 volt circuit) to a box with a 240 volt receptacle and a (or a pair of) 120 volt receptacle in it?
Multiwire branch circuit
Old 05-11-2011, 09:26 AM   #9
I=E/R
a7ecorsair's Avatar
In the opening post:
a7ecorsair is offline   Reply With Quote
Old 05-11-2011, 09:29 AM   #10
A "Handy Husband"
rjniles's Avatar
My answers in red
Missed that Allan.With a 4 wire he can add a sub- panel to replace the existing dryer receptacle.
A MWBC is used to get 2 120 volt circuits, not for both a 120 and a 240. If it is used for a 120/240 volt circuit it is not a MWNC
Old 05-11-2011, 09:40 AM   #11
I=E/R
a7ecorsair's Avatar
Richard
Need a joed or JV or brric or somebody to comment:
The OP whats to feed a two gang box as a MWBC with a split 120 volt receptacle and then tap the two hots for a 240 receptacle.
Electrically it would work but I can't believe it would be compliant.
Old 05-11-2011, 12:20 PM   #12
A MWBC is used to get 2 120 volt circuits, not for both a 120 and a 240. If it is used for a 120/240 volt circuit it is not a MWBC
Since I seemed to be getting conflicting answers, I googled some more, and found a site that discusses the NEC itself. (Thank you AllenJ for providing the proper name for this circuit so I knew 'what' to Google!)
A MWBC can indeed provide both 240 and 120, so long as the fault protection is correct. On a MWBC providing only 'out of phase' 120V service, that can be 'either' a double pole breaker or two single pole breakers with a handle tie. The NEC requires that a double pole breaker be used if the MWBC also provides 240V service.
Additional....
The googling also came up with a number of sites with arguments 'against' MWBC's, some saying that future editions of the Code should ban them completely. However, from reading the logic behind the argument it seemed to me that the objections are met by properly installed fault protection, and that the same potential exists within the panel box itself on 'any' pair of out of phase circuits if one circuit loses neutral continuity. After all, tracing them back, every circuit in the house is on a common neutral in the box.
Richard
Old 05-11-2011, 02:07 PM   #13
A "Handy Husband"
rjniles's Avatar
Richard
I would like to see the reference where you found this.
Old 05-11-2011, 02:44 PM   #14
Licensed Pro
Section 210.4 (C) Exception 2. Basically says you may use a MWBC for line to line loads IF you protect the circuit with a common trip double pole breaker.
Old 05-11-2011, 04:02 PM   #15
A "Handy Husband"
rjniles's Avatar
I have reread that exception and exception #1 about 3 or 4 times and do not believe the intent is to allow the use of multiple line to neutral and line to line loads on the same MWBC. Maybe we need input from one or more of the working electricians on this forum.
220v vs 110v Baseboard Heater?? Master Brian Electrical 8 11-20-2010 12:13 AM
220v to 110v extension cord? glamabilly Electrical 14 09-26-2010 12:25 AM
Main box feeding 220v and 110v brearker box off a 50am breaker? uvamosk Electrical 30 10-14-2009 11:46 PM
Adding 110V outlets to 220V line MarcG Electrical 25 04-29-2009 07:04 AM
Convert 220V to 110V wrldruler Electrical 13 09-15-2008 12:55 PM