220 Recepticle With 110 Current To Metal Box - Electrical - DIY Chatroom Home Improvement Forum
Old 01-12-2010, 09:41 PM   #1
220 recepticle with 110 current to metal box
Today I wired a single-phase 20 amp 220V 3-blade receptacle. After testing as expected, I got 220 V when both hot receptacle slots were tested. Also got 110 Volt from the ground receptacle slot to each of the hot wires slots individually. I have a metal receptacle box and happened to notice it registers 110 V when I touch a single hot receptacle slot and the metal box. I thought this odd since my ground is insulated and not a bare cooper wire. Is this normal? Does the female receptacle ground to the metal box? (no neutral was wired)
cwillard is offline   Reply With Quote
Old 01-12-2010, 09:48 PM   #2
Inspector/Instructor
codeone's Avatar
Yes this is normal if you grounded the box properly. The ground is to give you a low impedance path back to your panel so the breaker will trip if there is a short to ground, and so your body would be a higher impedance and not go back through you.
codeone is offline   Reply With Quote
Old 01-12-2010, 09:51 PM   #3
Thanks. I wouldn't have noticed except I just happend to touch the box while testing. Appreicate the info.
Old 01-13-2010, 12:23 PM   #4
Rewards Points: 78
All metal boxes should have a ground pigtail from the device (receptacle) to the metal box. There will be a 10/32 threaded hole in the box. Take a green or bare wire and a green grounding screw from this connection point to the grounded terminal of the receptacle. Yes, is the answer to your question.
Note: There are exceptions to this rule. But to be on the safe side, just install the jumper.
Tags
220 , 3-blade , box , single-phase
Ground rod or not? brotherman Electrical 30 07-15-2008 05:58 PM
Wire size for 300watt trans, 3 way 100ft Al the Diy guy Electrical 16 03-22-2008 09:46 PM
Sub panel grounding sluggermike Electrical 27 11-11-2007 02:23 AM