Originally Posted by kmatthews View Post
I had a feeling that something wasn't right. Just so I'll know when the next licensed electrician (yes, the electrician that ran the line was licensed) what type of wire should be used for a 220 outlet in ground? Should conduit be used irregardless of the type of wire? I live in Florida in an area with very high degree of lightning strikes. I was wondering if it would be safer with conduit. Thanks for the information. Although I'm a consumer, I've learned that I have to be somewhat knowledgeable or this kind of thing happens
First of all .,
I know you mention electrician but to bury that conductor only 6 inches deep that is not the legal way to do this.
A good electrician will stop right there and talk to you to change to proper conductor or UF cable.
In the conduit ( pipe ) the UF cable is allowed but it will be a bear to pull thru the conduit unless it is seriously oversized the most common methold is use the THHN / THWN conductors.
I did catch one part that you say kilns in there so therefore by the code you will defentally need a subpanel in the garage so per the NEC code you can have single MWBC ( Multi Wire Branch Circuit ) or single circuit but nothing more than that as I mention.
For the depth I know this is more than just a standard 20 amp circuit so bury the conduit minum of 18 inches deep or if you have UF then it will kick to 24 inch deep.
I think there is something more going on here with this set up what you have now.
If possible to post the photo then we can able assit you more on this matter.
As you mention the electrician buried 6 inches deep that part there is NO way a good electrician will do this at all ( I am not suprised if unliscensed handyperson done that and not follow the code at all that is typical which I get it pretty often either side of USA or in France )
Merci,
Marc
Old 05-27-2012, 09:50 PM   #17
retired elect/hvac/plumb
plummen's Avatar
Location: south east of omaha/The island of misfit contractors
Rewards Points: 2,020
It's buried only about 6 inches.
EEEEEEEEEEEEEEEEEEEEEEEEEEEEEEEEEEEEEEEk!
Id suggest a minimum of 18" even in conduit.
"facts" have no relevance to this discusion
Posting from a concrete bunker under a non descript barn
plummen is offline   Reply With Quote
Old 05-27-2012, 10:56 PM   #18
Electrical Contractor
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
So happy I insist on having all my buried electrical cable 24" below grade in conduit. So much easier having it out of the way. If the OP probably did not tell the irigation contractor about the feed and it was too shallow I don't understand how they can blame him.
With Electricity there is the right way to do it and the dead way. Just because it works does not make it safe.
rrolleston is offline   Reply With Quote
The Following User Says Thank You to rrolleston For This Useful Post:
plummen (05-28-2012)
Tags
220 , amperage , electrical lines , safety , splicing
Valid reasons why ground wires in a j-box would not be spliced together? buckybadger Electrical 6 12-12-2011 11:42 AM
max # of gauge AWG14 spliced amakarevic Electrical 4 11-03-2011 11:49 AM
Can garage feeder be spliced to SE once inside? WillK Electrical 5 05-27-2011 07:02 AM
Replacing Spliced Knob and Tube fromscratch Electrical 6 05-24-2011 08:04 AM
run spliced lamp cord inside a wall? denemante Electrical 20 12-17-2010 09:35 PM