220 Exterior Wiring being spliced
I'm having some irrigation installed. The installer cut through a 220 in ground line. They said it would be ok to splice it and put silicone around it. I'm concerned about the safety since the line is connected to an outlet in a detached garage that contains 2 kilns that run on the 220 circuit. The garage is about 50 feet from the house. Is it safe to splice the wire in three places in the manner described above? Should another line be run within conduit? Will splicing effect the amperage?
kmatthews is offline   Reply With Quote
Old 05-26-2012, 10:33 AM   #2
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Simply splicing the wires that were cut and siliconing the connections is not compliant. I always use a no heat, underground splice kit, but they do have heat shrink varieties as well.
I should ask, what type of wire was cut? Direct burial?
Old 05-26-2012, 10:57 AM   #3
What type of wire
In answer to your question regarding the type of wire and whether it was buried directly in the ground: the type of wire is Rouond NM-B cable, AWG 10-3 w/ ground, non-metalic sheathed cable. The cable was originally in a conduit pipe. The person who was making the repair did not put it back into conduit. Should the wiring be re-run? Thank you for your advice.
Old 05-26-2012, 11:07 AM   #4
Licensed electrician
Rewards Points: 1,478
Type NM-B is not rated for use outside or underground. It should not have been installed and should be replaced.
Since you have conduit this may not be that hard to fix by installing THWN conductors after patching the conduit.
The Following 7 Users Say Thank You to Jim Port For This Useful Post:
andrew79 (05-26-2012), frenchelectrican (05-27-2012), gregzoll (05-26-2012), J. V. (05-28-2012), k_buz (05-26-2012), plummen (05-27-2012), Speedy Petey (05-26-2012)
Old 05-26-2012, 11:27 AM   #5
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,948
It should be their responsibility to repair the conduit. NO question. DO NOT simply splice it outside the conduit.
It should then be your responsibility to replace the NM-B cable with the proper outdoor cable or conductors.
It's only 50'. That is not that big of a deal.
The Following User Says Thank You to Speedy Petey For This Useful Post:
J. V. (05-28-2012)
Old 05-26-2012, 12:14 PM   #6
220 in ground spliced wiring
I had a feeling that something wasn't right. Just so I'll know when the next licensed electrician (yes, the electrician that ran the line was licensed) what type of wire should be used for a 220 outlet in ground? Should conduit be used irregardless of the type of wire? I live in Florida in an area with very high degree of lightning strikes. I was wondering if it would be safer with conduit. Thanks for the information. Although I'm a consumer, I've learned that I have to be somewhat knowledgeable or this kind of thing happens
Old 05-26-2012, 12:52 PM   #7
Sparky
Rewards Points: 510
If a cable is used it should be type UF.
Individual conductors should be type THWN
Techy is offline   Reply With Quote
Old 05-26-2012, 01:03 PM   #8
Sparky
Rewards Points: 510
you also may have another violation (more than one circuit ran to a detached outbuilding)
Old 05-26-2012, 01:54 PM   #9
First off, there is no certain wire for a "220 outlet". I know this is a generalization, but I just want to clear this fact up.
Second, are you SURE it is NM-B and not UF? They look amazingly alike, especially when filthy.
The Following 2 Users Say Thank You to Speedy Petey For This Useful Post:
J. V. (05-28-2012), plummen (05-27-2012)
Old 05-26-2012, 02:48 PM   #10
Master Electrician
our underground wire up here is labelled nmwu for the most part. It's almost identical to regular nm except for a little thicker exterior rubber. It's generally black in color and indoor is generally white. You can incase it in conduit but it's not necessary although it will affect the depth it needs to be buried at. Personally if your going to run a conduit then do as the others have suggested and run thwn single conductors. Much cheaper.
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
Old 05-27-2012, 10:03 AM   #11
Splicing 220 wire
I don't really understand everything you all said completely, however I will keep the information so that I can refer to it when the worker comes back this week. I really appreciate the advice thank you for your time and expertise.
Old 05-27-2012, 05:40 PM   #12
Electrical Contractor
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
How deep was this buried?
With Electricity there is the right way to do it and the dead way. Just because it works does not make it safe.
rrolleston is offline   Reply With Quote
Old 05-27-2012, 05:56 PM   #13
How deep is wire buried?
It's buried only about 6 inches.
Old 05-27-2012, 06:13 PM   #14
Normal burial depth would be 12" if GFI protected and 20 amps or less, or 18".
Code05 (05-27-2012)
Old 05-27-2012, 07:32 PM   #15
No way this was done by any qualified electrician.
The Following 4 Users Say Thank You to Speedy Petey For This Useful Post:
Code05 (05-27-2012), frenchelectrican (05-27-2012), J. V. (05-28-2012), Jim Port (05-27-2012)
Tags
220 , amperage , electrical lines , safety , splicing
Valid reasons why ground wires in a j-box would not be spliced together? buckybadger Electrical 6 12-12-2011 11:42 AM
max # of gauge AWG14 spliced amakarevic Electrical 4 11-03-2011 11:49 AM
Can garage feeder be spliced to SE once inside? WillK Electrical 5 05-27-2011 07:02 AM
Replacing Spliced Knob and Tube fromscratch Electrical 6 05-24-2011 08:04 AM
run spliced lamp cord inside a wall? denemante Electrical 20 12-17-2010 09:35 PM