220 Air Compressor - Electrical - DIY Chatroom Home Improvement Forum
Old 11-03-2012, 10:38 AM   #1
220 air compressor
can a 3 phase motor be hooked up with 1 phase
tyson1964 is offline   Reply With Quote
Old 11-03-2012, 11:02 AM   #2
Julius793's Avatar
Won't work
Electricity will kill you if you give it a chance
Julius793 is offline   Reply With Quote
Old 11-03-2012, 11:23 AM   #3
Rewards Points: 126
Yes. But you need a rotary converter or a VFD. The VFD is much less expensive, but can only power the motor. Nothing else. You can input 120 or 240 single phase and get either 230 or 460 3 phase out with a VFD.
Old 11-03-2012, 11:27 AM   #4
where can i get a VFD
Old 11-03-2012, 11:36 AM   #5
Rewards Points: 13,450
Google static phase converter.
MSC, McMaster Carr are two places that have them.
They will reduce the HP by about 50% for they may or may not even start the motor.
A rotary phase converty is far better but there expencive. They also can be used to start more then one piece of equipment if there started one at a time as long as the HP is less then what the converter is rated for.
tyson1964 (11-03-2012)
Old 11-03-2012, 12:05 PM   #6
JOATMON
ddawg16's Avatar
Rewards Points: 1,452
Along with what Joe said....be aware that your going to need a lot of power. Look at the FLA on the existing motor. Lets use 10A at 240Vac 3ph, as an example...it will take a little about 4100w of power.
To get that power out of 240vac single phase you need over 17A at 240Vac.....as well as the extra power to run the VFD electronics (plus losses)....so I would estimate at least 20-25A at 240vac.
When you consider the cost of a VFD or phase converter.....you might actually be better off replacing that 3ph motor with a single phase 240Vac motor. In the long run it will be simpler and more reliable.
ddawg16 is online now   Reply With Quote
The Following 2 Users Say Thank You to ddawg16 For This Useful Post:
Old 11-03-2012, 01:22 PM   #7
Idiot Emeritus
Rewards Points: 1,492
Also, VFDs with single phase input get expensive over 3 HP.
A lot of larger VFDs will accept single phase input, but they need to be derated to about 1/2 of their 3 phase rating.
If you do indeed use a VFD, there will be some control issues you'll need to deal with. They're not plug and play.
To determine how difficult it will be to change the motor, look at HP, RPM, and Frame size. Since the existing motor is 3 phase, it is likely a standard NEMA frame, so a single phase replacement (10HP and smaller) will be easy to find.
micromind is offline   Reply With Quote
The Following User Says Thank You to micromind For This Useful Post:
Old 11-03-2012, 08:04 PM   #8
Semi-Pro Electro-Geek
Rewards Points: 2,922
I have had good results using the Hitachi drives for small 3-phase motors on single phase power. Unlike "static phase converters" (which do not really produce 3-phase power), using a VFD will provide full rated motor power and also give you advanced control over the operation of the motor. It's great. For motors 3HP and less, I'd rather have a 3-phase motor with a VFD than a single phase motor. For larger motors it's hard to find VFD's that will accept a single phase input. You can usually trick larger VFDs into working, but you have to under-rate them by at least a third.
Here's a 3HP VFD that I have used for a few years on an outdoor pump in Arizona. It's held up fine:
http://www.driveswarehouse.com/p-212...0-022nfu2.aspx
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is offline   Reply With Quote
The Following User Says Thank You to mpoulton For This Useful Post:
Air Compressor Fittings - Differences? roasted Tools 3 09-19-2012 08:15 PM
Help assembling compressor jfhspike Tools 5 03-27-2011 10:07 AM
Air compressor and framing nailer for DIY ADKstorm Tools 20 11-11-2010 07:38 AM
Please help: blown fuse, slow compressor fan, and hissing noise from compressor frazwr01 HVAC 10 06-27-2010 09:08 PM
New Compressor - Wrong Charge? shayneb HVAC 4 08-23-2008 08:13 AM