20a switch in a 15a circuit?
Hi all, first time poster here. I am trying to replace all my receptacles and switches in the house and have a small question. I know that it's ok to use 15a receptacles on 20a circuit.
Is it ok to do the opposite? 20a receptacles on 15a circuit? - I asked because there's a sale on the 20a receptacles.
Likewise, there's also a sale on 20a switches (single pole on/off and single pole 3-way). I don't know whether the switches in my house are 15a or 20a and wants to know if using a 20a switch is ok or not.
One last question, I really like the Leviton Acenti lines of products but they are expensive, is there a place that I can get them at a better price point?
Thanks,
syzygylock is offline   Reply With Quote
Old 06-10-2009, 03:37 PM   #2
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,214
Originally Posted by syzygylock View Post
Hi all, first time poster here. I am trying to replace all my receptacles and switches in the house and have a small question. I know that it's ok to use 15a receptacles on 20a circuit?
15 amp receptacles on 20 amp circuits are fine. (Reason is you cannot plug a 20 amp plug into a 15 amp recp.)
20 amp recp. on 15 amp circuit is a no. (Reason you could plug a 20 amp plug into a 15 amp circuit)
20 amp switches are fine for 15 or 20 amp circuits. (Reason you don't plug anything into a switch)
Old 06-10-2009, 03:41 PM   #3
300zx's Avatar
Post
posted before i could,Good Reply
300zx is offline   Reply With Quote
Old 06-10-2009, 03:46 PM   #4
Ah great, thank you very much
Old 06-10-2009, 03:56 PM   #5
DIY'r
ScottR's Avatar
Can't hurt to go with 20A switches when buying in bulk.. if only so that you don't have to worry about whether each circuit is rated @ 15 or 20A when you install them.
Aye, but you may plug something into a receptacle that's controlled by a switch..
ScottR is offline   Reply With Quote
Old 06-10-2009, 04:01 PM   #6
Which brings you right back to the outlet being either 15a or 20a rated per the circuit rating
I think they make 20a rated outlets that do not have the T slot tho?
Old 06-10-2009, 04:09 PM   #7
DIY'r
ScottR's Avatar
I was thinking along the lines of that's why you shouldn't put a 15A switch on a 20A circuit even if the lighting load is "only" 100W or some such..
I was just not following why rjniles said that.. he was, of course, correct in his reasoning.
Old 06-10-2009, 07:19 PM   #8
joed's Avatar
Rewards Points: 12,862
There is a difference between a 20 amp receptacle and a 20 amp rated pass through. A 20 amp receptacle has a different pin configuration(one pin is sideways). A 20 amp rated pass through has terminal connection rated for 20 amps so they won't burn up when used on a 20 amp circuit.
The current rating of a switch is always a maximum rating of the maximum current it can switch without burning up the contacts.
Old 06-10-2009, 08:07 PM   #9
Bigplanz's Avatar
Rewards Points: 990
Is it a code violation to put a 20A receptacle (T-slot) on a 15A circuit? If it is, I can't find it. If you plugged in a 20A device (I can't say I have ever even seen a device with a T-slot plug) the worst that would happen is the breaker would trip. It doesn't make any sense to do this, but if it's a violation, I can't find it in the NEC. If it is, someone please post the citation. Thanks.
Bigplanz is offline   Reply With Quote
Old 06-10-2009, 08:25 PM   #10
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,956
It is a violation for a circuit with more than one receptacle (even one duplex).
See NEC Table 210.21(B)(3) & T210.24
A single receptacle on an individual branch circuit must have a rating of not less than that of the circuit rating. So a single 20A receptacle is OK on a 15A circuit. This is why you mainly see simplex receptacles in the 15/20A dual configuration as opposed to true 15 or 20 amp.
See NEC 210.21(B)(1)
Old 06-10-2009, 11:34 PM   #11
Actually you can put a 50 amp outlet on a 15 amp circuit. I don't know why you would. The rating of the circuit is measured against the lowest rated component not the highest. If you have a 15 amp breaker and you connect a 50 amp load in it would just trip the breaker. So yes you can install 20 amp receptacles in a 15 amp circuit.
hayewe farm is offline   Reply With Quote
Old 06-11-2009, 06:39 AM   #12
Not if there is more than one receptacle on the circuit.
See my last reply and code reference.
Just for fun Andy in ATL Electrical 56 10-20-2009 09:33 AM
Replacing a bathroom fan switch cmacjr22 Electrical 4 11-04-2008 06:14 PM
Wiring a single pole switch into a 220v circuit rlmorgan Electrical 38 10-15-2008 07:59 PM
4 Way Switch Circuit Gone Wrong AbSoluTc Electrical 11 01-26-2008 02:57 PM
adding 3-way switch to existing circuit msahaydak Electrical 4 02-18-2007 12:43 AM