20A GFCI On 15A Circuit - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 10-15-2008, 08:26 PM   #16
Electrician
Originally Posted by HouseHelper View Post
I believe you are confused. You can put a 15A receptacle on a 20A circuit if you have two or more, but you cannot put a 20A receptacle on a 15A circuit, no matter how many you have.
But as others have said, in this case, you can live with it until the correction is made.
Nope, not confused brother, I can easily install a 20 amp single receptacle on a individual 15 amp circuit.
Check out 210.21(B)(1) and read it about 20 times... Bawhahahah...
chris75 is offline   Reply With Quote
Old 10-15-2008, 08:37 PM   #17
Registered User
Termite's Avatar
I've been accused of being unreasonable from time to time on inspections, but that's one thing I'd never turn somebody down for (20 amp rated receptacles on 15 amp circuits).
I just have a hard time figuring out the hazard.
Old 10-15-2008, 08:37 PM   #18
Res Ipsa Loquitur
Originally Posted by jbfan View Post
You will find very fews things to be used in a home with a 20 amp plug.
Correct and certainly not one to plug in a bathroom!
I'm thinking of compressors, air conditioners, high draw items.
Did you ever stop to think, then forget to start again?
handyman78 is offline   Reply With Quote
Old 10-15-2008, 08:40 PM   #19
Electrician
Its not a hazard, but lets play fair, a violation is a violation.
Old 10-15-2008, 09:17 PM   #20
Licensed Pro
It only took once. I'll blame it on a senior moment.
Old 10-15-2008, 09:34 PM   #21
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,824
Sorry Chris, you are wrong on this one.
Go back and re-read the two charts very closely.
The first column in Table 210.21(B)(2) is the circuit rating, not the receptacle rating.
Synopsis:
Total Cord-and-Plug-Connected Load
Table 210.21(B)(2)
Circuit rating: 15 or 20, Receptacle rating: 15A, maximum c&p connected load:12A
Receptacle Ratings
Table 210.21(B)(3)
Circuit Rating: 15A, Receptacle Rating: NOT OVER 15A
Circuit Rating: 20A, Receptacle Rating: 15A or 20A
Old 10-15-2008, 09:48 PM   #22
DIY'r
ScottR's Avatar
I'm looking at the code (2008), and the text of 210.21(B)(3) says "Where connected to a branch circuit supplying two or more receptacles or outlets, receptacle ratings shall conform to the values listed in Table 210.21(B)(3) [...]"
So wouldn't that imply that if it were 1 receptacle on 1 circuit, the table is irrelevant, and 20A recep. on a 15A circuit is OK?
I'm confused anyway because 210.21(B)(3) allows a 50A recep. on a 40A circuit, but not a 20A on 15A circuit. But it allows a 15A recep. on a 20A circuit, which is counter intuitive..
ScottR is offline   Reply With Quote
Old 10-15-2008, 09:53 PM   #23
Yes, a GFI is "more than one receptacle". It is TWO receptacles outlets in one device.
This is why a SINGLE, or simplex, receptacle is dual slotted for 15 & 20 amps. Both 120v and 240v come like this. NEC 210.21(B)(1)
Old 10-15-2008, 09:53 PM   #24
DIY'r
ScottR's Avatar
Are you sure. The code says a single receptacle must have an ampacity not less than the rating of OPD.
If the receptacle is 20A and the OCPD is 15A, then it would be OK according to the above..
Old 10-15-2008, 09:55 PM   #25
Scott, there was just a post there by Jerry @9:51pm that disappeared. Creepy.
Old 10-15-2008, 09:58 PM   #26
Jerry learned how to read and corrected his post.
jerryh3 is offline   Reply With Quote
Old 10-15-2008, 09:59 PM   #27
DIY'r
ScottR's Avatar
I retract my previous statement...
Old 10-15-2008, 10:01 PM   #28
DIY'r
ScottR's Avatar
I saw it, but I guess Jerry's solved the mystery.. I thought that was weird too.
Old 10-15-2008, 10:43 PM   #29
Electrician
okay, what did I miss? All I am saying was that if I install a 20 amp single receptacle on a 15 amp individual circuit, that it meets code, 210.21 (B)(1) allows this. You dont need to read anything else BUT 210.21 (B)(1) because the other sections do not apply.
Old 10-15-2008, 10:45 PM   #30
Electrician
Synopsis:
Table 210.21(B)(2)
Receptacle Ratings
Table 210.21(B)(3)
I'm not wrong and I can prove it. First off, why are you even looking at tables (B)(2) and (3) ? Read (B)(1)
new gfci on new circuit pops rtoni Electrical 39 11-15-2008 11:18 AM
Testing circuit with GFCI protection Hodag Electrical 4 09-15-2008 11:43 PM
Microwave trips GFCI on a different circuit! Frank Kolwicz General DIY Discussions 7 06-01-2008 09:48 PM
GFCI circuit Cossack Electrical 31 03-21-2008 01:34 AM
GFCI and Smoke alarm circuit issues 00u6166 Electrical 9 10-30-2007 03:41 PM