208V IR Heater On 240V? - Electrical - DIY Chatroom Home Improvement Forum
Old 07-31-2011, 12:01 PM   #1
208V IR heater on 240V?
I'm moving my shop. At the old shop I have 208 3-phase with a 208V leg. AT the new shop, I have 240V 3-phase with a 240V leg.
I have two infrared heaters that have two elements each that share a common connection. I currently have each element connected to a single-phase 208V.
Will each element be OK on a 240V circuit?
hduff is offline   Reply With Quote
Old 07-31-2011, 12:10 PM   #2
Rewards Points: 1,512
Check the voltage rating on a sticker or name plate anyway. It may well have been a 240 volt heater to begin with. Do not run a 208 volt only heater on 240 volts if it has moving parts such as a motor.
There is a small chance that the life span will be shortened just a little for a 208 volt heater run on 240 volts. It will be hotter on 240 volts compared with on 208 volts.
By the way you will get 208 volts if you connect something from the 120/240 volt delta 3 phase neutral to the wild leg, the latter often with wires marked in orange. Do not use 120 volt receptacles if you run a branch circuit using the wild leg and neutral.
Old 07-31-2011, 02:32 PM   #3
biggles's Avatar
how true was the 208.... 213 216?? then the 240 will always be lower range 235 just the amps will change to less read compared to 208
Old 07-31-2011, 05:28 PM   #4
Semi-Pro Electro-Geek
Rewards Points: 2,938
Many (probably most) heating appliances are rated for both 208 and 240V operation. Even if it's not, any 240V-rated heater can be run on 208 at reduced power. However, a 208V-only heater on 240V will run at 33% higher power and this could cause overheating. So, what does the rating plate on it say?
mpoulton is offline   Reply With Quote
Old 07-31-2011, 05:33 PM   #5
This is a passive infrared heater with no moving parts, just two elements with two wires each.
I'll have to find my 12' ladder and look at the units when I remove them to see if they are rated for other than 208V.
Pilot on Williams millivolt wall heater goes out every 8 to 16 hours wornways HVAC 30 06-22-2011 03:29 PM
Noma fan forced wall heater 240v Stevec1234 Electrical 9 03-12-2011 05:30 PM
Replacing 240V Wall Heater with 240V Base Board Heater jasoncw Electrical 7 11-26-2010 10:39 AM
Problem with 240V Elect Baseboard Heater JRHP Electrical 4 10-04-2010 09:30 AM
wiring a 240V baseboard heater 777 Electrical 10 05-17-2009 10:47 AM