208v Heater - Electrical - DIY Chatroom Home Improvement Forum
Old 04-19-2009, 03:35 PM   #1
208v heater
how do i wire a dayton 2yu68 208v 7.5kw 60hz heater in my garage?also the heater shows .6 in the amps box is this correct
phil dufour is offline   Reply With Quote
Old 04-19-2009, 04:06 PM   #2
General Contractor
HWConstruction's Avatar
You will have to wait for one of the sparkies to give you the right answer but..... If I'm right you have to get a transformer because 208 volts is gotten from 3 phase power witch you don't have at a residence.
HWConstruction is offline   Reply With Quote
Old 04-19-2009, 04:24 PM   #3
7500/208 = 36a.
Old 04-19-2009, 04:29 PM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,992
No, .6A is not even remotely close. That heater will draw 36A @ 208v.
That same heater will provide approximately 10kW wired at 240v and draw approximately 42 amps. This will require a 60A circuit.
The fan will most likely be fine at 240v so you should be OK, but 10kW is a bunch of heat. Do you really want to use electric heat?
Old 04-19-2009, 04:33 PM   #5
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
It also has a 24 volt contactor coil but it doesn't say whether a transformer is included. I'd take it back and get the 2YU66 or 69. If you got it from WW.
wirenut1110 is offline   Reply With Quote
Old 04-19-2009, 06:17 PM   #6
so the heater can be wired to 240v at 60 amp breaker? it will only be used as a secondary heat sourse so electric heat is ok.also you said i need a transformer there is something in the heater that says attach thermostat wire here at two terminals and has a 24v tag on it
Old 04-19-2009, 09:47 PM   #7
Electrician
Rewards Points: 802
You need a 24V thermostat and you can use #18 wire for this.
darren is offline   Reply With Quote
Water heater drain mechanism (10 year old) guptaalok Plumbing 1 01-02-2009 05:40 AM
Water heater problem bear1957 Plumbing 23 11-01-2007 03:53 PM
Baseboard heater Help! jweinstock Electrical 6 10-28-2006 04:01 PM
Periodic release from (I think) the T&P valve on the water heater alexz Plumbing 3 08-15-2006 10:31 AM