208 volt delta transformer or 208V Y
is 208 a volt delta transformer used , if the service is going to be 280/120V-3P-4W and would like 480/277V-3P4W or will you need a 208 Y to 480/277 WYE transformer?
joe niemczyk is offline   Reply With Quote
Old 10-25-2012, 07:41 PM   #2
Idiot Emeritus
Rewards Points: 1,492
If you want 277/480 and you have 120/208, the best transformer would have a 208 delta primary and a 277/480 wye secondary.
With this transformer, you'd need only the 3 phase wires from the 208 system, not the neutral. The 480 side would have 3 phase wires plus the neutral. Do not connect the neutral from the 208 system to the neutral of the 480 system. The ground is the only connection between the two.
Rob
micromind is offline   Reply With Quote
Old 10-25-2012, 07:47 PM   #3
Semi-Pro Electro-Geek
Rewards Points: 2,856
The NEC (and safety) requires that the secondary neutral be bonded to ground. Thus, the primary and secondary neutrals will be connected to each other through their respective bonds to ground.
It's generally considered best to use a delta primary and wye secondary. If you use a wye primary though, you must connect the neutral - you can't leave it floating.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is offline   Reply With Quote
Transformer Question Delta to Wye D-Wade Electrical 3 07-24-2012 07:37 PM
Low Voltage Transformer Problem dlp710 Electrical 2 07-06-2012 10:56 AM
12 Volt lighting AC or DC johnr9q Electrical 20 11-21-2010 02:12 PM
wiring a 220 volt delta unisaw and delta x5 planer naveall Electrical 13 10-30-2008 02:30 PM
Central Ac transformer question Rschrei518 HVAC 4 10-20-2008 09:21 PM