-   -   208/230 vs 115 (http://www.diychatroom.com/f18/208-230-vs-115-a-106367/)
zephed666 06-02-2011 12:58 PM
208/230 vs 115
Hello:
I have a question about 208/230 voltage as opposed to 115v. I am trying to replace an AC for my home and the unit either come in 208/230 or 115. I currently have a dedicated 20A single pole breaker for the exsiting unit. Does that mean I need to go with the 115v unit?
Thanks!
jbfan 06-02-2011 01:08 PM
If you only have a single pole breaker, then you can only install a 120 volts ac.
If you have room to add a 2 pole breaker, then you can use a 240 volt ac.
rjniles 06-02-2011 01:11 PM
What is the amperage requirements for the 208/230 connection? for the 115 connection?
If you have a single pole 20 amp breaker (hopefully wired with 12-2 wire) you cannot exceed the 20 amps.
If it is more than 20 amps (@120 Volt) , you will have to go with the 208/230 option. That means changing out the breaker to a 2 pole device and rewiring in the main panel.
Answer the first 2 questions and we can be more specific.
Is this a unit made in the US, because 230 or 115 are not standard voltages for US. 240 and 120 are the standards.
AllanJ 06-02-2011 04:47 PM
230 volt and 230/208 volt equipment will work perfectly well on 240 volts.
115 volt equipment will work perfectly well on 120 volts.
120/240, 110/220, and 115/230 volt equipment must not be connected to a circuit with 208 in its designation unless you have insider information that it will work that way.