200Amp Panel In New Construction - Electrical - DIY Chatroom Home Improvement Forum
Old 06-11-2014, 02:37 PM   #1
200Amp panel in new construction
Hi,
I am building a new house where one 200amp main panel and one 100amp sub panel are supposed to be installed. If electrician decides to install only one panel should it be a 300amp panel? how does this work? and is it cheaper for him to install only one panel?
Thanks.
nycdude2 is offline   Reply With Quote
Old 06-11-2014, 02:48 PM   #2
Remodel and New Build GC
MTN REMODEL LLC's Avatar
Rewards Points: 3,784
Well .... Under your current design you will have 200A service that goes all sorts of places, one of which is to another distribution panel (called a subpanel) and they happen to be sending 100A to it to go to subsequent places (branch circuts) They are not additive. (I assume your load calc are fine with 200 Amp service.
Your subpanel is put in for various reasons.... extra distribution capability (more breakers for more branch circuits) but also sometimes it is smarter anjd less expensive and better performance (less voltage drop) to wire in a subpanel with "big" wire, and then your subsequent branches will not have to run all the way back to the main/service panel (homerun).
Subpanels are not expensive.... probably $100.
MTN REMODEL LLC is offline   Reply With Quote
Old 06-14-2014, 09:48 AM   #3
Rewards Points: 924
Who designed it? and electrician can't just change the design without an approval. Don't be swayed by cheaper cost and insist on city inspection. Everything takes longer and costs more in nyc, but that's the cost.
carpdad is offline   Reply With Quote
Old 06-14-2014, 08:12 PM   #4
DIY staff
Rewards Points: 7,174
I moved this to 'electrical' for you---
Old 06-14-2014, 08:25 PM   #5
Rewards Points: 3,396
Little more.
Panel, breaker, wire, fittings, labor, getting it, delivering it to job in vehicle, gas, insurance, wear and tear, business insurance, compensation, taxes, and licensing to install it.
But yes. the actual panel is about 100. What make?? lol
ritelec is offline   Reply With Quote
Old 06-14-2014, 09:39 PM   #6
Msradell's Avatar
Rewards Points: 332
Originally Posted by ritelec View Post
Little more.
Actually, all the costs you mentioned should be a wash. The house is going to meet the same number of circuits thus the same number of breakers no matter which way it is done. It quite possibly will take less wire with a subpanel but even if it doesn't the subpanel option shouldn't cause any more than a larger main panel and it had to be designed in for a reason!
Msradell is offline   Reply With Quote
Old 06-15-2014, 09:05 AM   #7
Actually.
The location of the sub panel was never mentioned. Could be next to the main or 80' away.
Actually, someone, maybe an engineer, may have drawn up some prints and indicated circuits which where light. Maybe the electrician added and regrouped devices on circuits to cut down on them. Especially with the price of afci breakers.
All speculation.
And
"the wash"
I wash all the time so don't tell me about "the wash".
"the subpanel option shouldn't cause any more than a larger main panel"
I've only seen 200 amp in residence so what do you mean "larger"
A 30 something or 40 circ 200 amp panel is going to be ~ $200.
A aub panel which ever size will always cost something, it's not free.
Add the breaker to feed it, and wire, and labor to install.
One or Two panels is not the same cost.
Oh. forgot "the wash".
All in all we don't know the real situation.
The op may have thought and should have gotten a sub panel.
Maybe it didn't really need it, and maybe the electrician did something else for him.
Maybe not.
We are only speculating.
Old 06-15-2014, 11:55 AM   #8
Rewards Points: 131
If the load calc is good for 200 amp and they just need extra space. . .something like a seimens 42/60 panel could work. Don't think it would save any $$.
http://www.amazon.com/gp/aw/d/B005GL...&robot_redir=1
If the second panel is designed to be in a separate area of the house to conserve wire and reduce voltage drop, then it may be necessary. If it it's a 4000+ sf home, maybe that's the case.
Sent from my SCH-I535 using Tapatalk
b4bhomeowner is offline   Reply With Quote
The Following User Says Thank You to b4bhomeowner For This Useful Post:
Cletis (06-15-2014)
Old 06-15-2014, 03:05 PM   #9
Rewards Points: 1,832
Well it boils down to 2 things. Cuicuits and the amount of power required. If the home requires a 300amp service one could install 2 200amp panels from double lugged meter socket or a 320amp (technically 400amp) panel. Its generally cheaper to do 2 200amp panels and use SEU since the price of a 400amp single phase panel tops 2 smaller ones.
If 200amps is enough for the house all you need is one 200amp panel. Then we go to spaces (circuits) If more than 42 circuits are needed you can now buy a 60 or 80 circuit panel since the 42 circuit rule was deleted in the NEC. Of course, if going a sub panel route, that is doable also in both scenarios.
Jump-start is offline   Reply With Quote
Old 06-16-2014, 08:59 PM   #10
could you send me a link so I could see a 400 amp single phase panel please.
I've never seen one.
Thank you.
Old 06-16-2014, 11:27 PM   #11
Thank you.
Sure because I make everything up as I type:
Old 06-16-2014, 11:30 PM   #12
Thank you.
Heres another one:
http://www.ebay.com/itm/Square-d-NQ-...item3a91c5ee7f
200Amp panel in new construction-nqod001.jpg   200Amp panel in new construction-nqod1.jpg
Old 06-17-2014, 05:40 AM   #13
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Thank you.
They make 400 amp transfer switches as well....
Old 06-17-2014, 07:33 AM   #14
Thanks.
Again NEVER seen one.
Now I have.
Old 06-17-2014, 07:37 AM   #15
(thinking about this, how do I know you didn't photoshop a 3 phase panel?)
Multiple Panel Question theatretch85 Electrical 7 09-29-2016 07:15 PM
Panel clearance requirements & workbench construction WillK Electrical 1 06-26-2011 11:56 PM
Wiring a sub panel to another sub panel Uncle Wayne Electrical 25 02-08-2011 09:50 AM
Replacement Meter Panel leonard_voet Electrical 19 04-09-2008 10:27 AM
In-line fuses used on GE 200amp panel instead of main breaker diyforum Electrical 4 11-07-2007 07:08 PM