Old 12-27-2010, 02:20 PM   #1
2000w heater on 15A-240v
Hello, is it acceptable to have a 240v, 2000 watt fan forced heater running on 14/2 wire and two 15A circuits?
DragonFire is offline   Reply With Quote
Old 12-27-2010, 02:23 PM   #2
the Musigician
DangerMouse's Avatar
ummmm.... I'd guess no......
Do I win a prize?
DM
[SIGPIC][/SIGPIC]Click
to see some of my original magic tricks and trick boxes!
Old 12-27-2010, 02:25 PM   #3
Master Electrician
2000 watts @ 240 volts equals 8.3 amps. Are you asking about a 2 pole circuit breaker and calling it 2 15 amp circuits?
brric is offline   Reply With Quote
Old 12-27-2010, 02:27 PM   #4
A "Handy Husband"
rjniles's Avatar
A 15 amp, 240 volt circuit is capable of 3600 watts. Well within the heater at 2000 watts. If by "two 15A circuits" you mean 2 15 amp circuit breakers there may be a problem. If it is 2 seperaate single pole breakers they must be side by side and connected with a handle tie so both turn off at the same time or use a single 2 pole, 15 amp breaker.
Coastal South Carolina
rjniles is offline   Reply With Quote
Old 12-27-2010, 02:34 PM   #5
Master Electrician
This application would absolutely require a 2 pole circuit breaker and NOT 2 single poles with a handle tie. It is NOT a MWBC.
The Following User Says Thank You to brric For This Useful Post:
clashley (12-27-2010)
Old 12-27-2010, 02:46 PM   #6
Thanks, just out of curiosity what could happen if 2 single 15amp circuits were used in this application, and were not side by side?
Old 12-27-2010, 02:53 PM   #7
Electrical Contractor
Fire, smoke and the IRS may visit!!
If they are not on a 2 pole breaker, and side by side, you Will have issues in the future!
Someone(meaning you) may need to swap breakers around and put them on the same leg, thus having no heat.
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
Old 12-27-2010, 02:53 PM   #8
Master Electrician
If they're on the same buss then nothing will happen. There will not be any current flow.
Old 12-27-2010, 03:00 PM   #9
... the double-pole breaker thing is a code requirement - a law of the government, not a law of physics.
If you have two single-pole breakers on opposite legs, the heater will work. In the event of a fault, it will be the same as protecting it with two seperate fuses, which IS legal. If the fault is to ground, ONE breaker will trip and the other may not, meaning that the heater may stop working, and one breaker may be tripped, but the heater may still be "live" on one end. The "danger" this creates is to the person who comes along attempting to fix said heater, believing the power to be off, and discovers the hard way that it is not so.
Put another way, as long as everything remains in good condition (and I mean internally as well), nothing bad will happen, but it's not a good idea, because someday, sooner or later, something will "wear out" (or otherwise expire) and potentially cause an unexpected condition.
Having one double-pole breaker ensures that ANY overcurrent/short fault will turn off the heater ENTIRELY.
emolatur is offline   Reply With Quote
Old 12-27-2010, 03:10 PM   #10
Master Electrician
Yes it will work. IT IS A CODE VIOLATION.
Old 12-27-2010, 03:43 PM   #11
This particular application is considered a 240V circuit, which requires a double-pole breaker by code. Using two tied single-pole breakers is only appropriate for a 120V MWBC, which requires a properly-pigtailed common neutral. The OP's 240V application does not require a neutral and therefore does not qualify as an MWBC. Code requires a double-pole breaker, similar to a WH.
While two stacked single-pole breakers would technically work in this situation, it increases the possibility for a later homeowner to rearrange the circuits incorrectly, since it might not be obvious why the breakers were arranged that way originally. Hence the code.
That being said, a 15A double-pole breaker would be appropriate for this situation.
clashley is offline   Reply With Quote
Old 12-27-2010, 03:58 PM   #12
Thumbs down
Thanks for all the great information guys. A further theoretical question.... is there any significant difference in the following 3 install scenarios for a 240v heater:
--2 single stacked 15amp circuit breakers
as opposed to
--2 single 15amp circuit breakers being non-stacked (ie slot #1 and #3 in the same side of the service panel)
as opposed to
--2 single 15amp circuit breakers on opposite sides of the service panel
Again, these are theoretical questions, as I completely understand the requirement for a 15amp double-pole breaker in my original question.
Old 12-27-2010, 05:20 PM   #13
as opposed to
as opposed to
--2 single 15amp circuit breakers on opposite sides of the service panel .
Whether each of these works electrically depends on the way the inside of the panel is constructed which in turn can vary from one model to another.
Two single stacked breakers (or the code compliant double wide 2 pole breaker) almost always yields 240 volts because the fins underneath the breakers in the panel are usually arranged with the odd rows on one side of the line and the even rows on the other, as:
AA
BB
AA
BB
Non-stacked, e.g. rows 1 and 3, usually don't yield 240 volts although once in awhile they might (if the fins are arranged:
AA
AA
BB
BB
AA
AA )
On the same row on opposite sides of the panel usually does not work but might if the fins are arranged something like:
AB
BA
AB
BA
The disadvantages of crab apple trees. In summer, the apples are too sour to pick and eat. In winter the birds come and leave dropping all over the place.
Old 12-29-2010, 12:05 PM   #14
Thank you, brric and clashley, for agreeing with me. Perhaps next time a closer read of my post will result in a less-argumentative tone to your confirmations, however.
While we're on the subject, and this is for academic purposes only, I do have to raise the situation of a 240V circuit drawn from a fuse box. It is, as you know, virtually impossible (or at least very difficult) to manufacture two fuses with a "common trip", so a fault to ground will quite likely leave the other side energized...
Pilot on Williams millivolt wall heater goes out every 8 to 16 hours wornways HVAC 30 06-22-2011 04:29 PM
Replacing 240V Wall Heater with 240V Base Board Heater jasoncw Electrical 7 11-26-2010 11:39 AM
Problem with 240V Elect Baseboard Heater JRHP Electrical 4 10-04-2010 10:30 AM
wiring a 240V baseboard heater 777 Electrical 10 05-17-2009 11:47 AM
240V Electric Heater install - 3 wire vs. 4 wire? dhgarage Electrical 7 12-12-2008 11:49 PM